Not quite it though looking at it. It gives the values of volts and amps etc. but not the capacitance for the "third" phase calculation unless I am missing something.
 
Do you mean for running a 3-phase motor from a single-phase supply?
 
So I take the 3 cross linked (two links) on the star configuration, and move the links directly down to the terminals on the other side and place L on one terminal and N on the other terminal I need a connection the third coil usually a capacitor taken from on of the other terminals depending on rotation required. So as to provide power to the third coil.
 
How many wires do you have access to
Not sure yet, but think I may have to place a capacitor in a three phase motor converting it to single phase. I presume I will see six wires three incoming and three linked as set up for three phase star configuration. Then I got to thinking what value capacitor for the (say)mid point connection. I suppose I can ask the motor manufacturer. They supply a wiring diagram but not the capacitor. I am not even sure yet what I will be dealing with as I have not looked at the connection but what else can it be after all. Assuming it's a bog standard wiring/motor 3 coils etc.
 
There is no one ideal value as the third leg current depends on the mechanical load, and if this is highly variable a compromise value is needed. The motor will always be running under abnormal conditions and its performance and power will be reduced.What is the application?
 
It's a 2Hp 9a 2Kw motor for irrigation on a farm. It may be it is single phase so nice and simple I am not sure if they send them all out as three phase or what at the moment awaiting more information.
 
So this pump will pump clean water to the field and has a Domino UP controller which is really just a fancy switch(ing) system to control and alarm running dry, or managing other switches such as float switch or pressure switch (Danfoss KPI35) for the expansion tank. I realise the float switch may be redundant. The Domino checks dry running through setting the Cos/Phi level at the motor.
 

Reply to Calculation of capacitor value for conversion from star to delta in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
621
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
674
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
961
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
683

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock