  1. Adam888
    Offline

    Adam888 New EF Member

    Location:
    Denbigh
    There is a double socket on the wall where the main feed comes in and this is then connected to a none switch fused socket. Iv'e been told i can add a other fused switched socket and connect both together then run 2 additional sockets off the fused switch one?
     
  2. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    Welcome to the forum mate.
    What do you mean by a "none switched fused socket"? Do you mean one of these?
    upload_2019-2-10_9-18-55.png
    Does the circuit you are adding to have RCD protection?
    Does the way you intend to add the extra sockets need the wires to have RCD protection?
    We need more info mate.
     
  3. Cid
    Offline

    Cid Regular EF Member

    Location:
    London
    You can't spur of a spur. Only one fused spur allowed of a socket.
     
  4. l4urence
    Offline

    l4urence Regular EF Member

    Location:
    East Sussex
    Note @Spoon@Spoon comments. The non-switched 'fused socket' is confusing the question unless it looks like the item pictured.
     
  5. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Change the original Spur for a fcu, then the world is your Oyster
     
    • Agree Agree x 1
  6. l4urence
    Offline

    l4urence Regular EF Member

    Location:
    East Sussex
    I'm looking again at the original question.
    why would you want to add another fused connection after the first?
    so:
    ring socket <---xFCUx---xSKTx---xSKTx
    if those sockets take more than the first 13A fuse they will stop (fuse blows).
    so:
    ring socket <---xFCUx---xSKTx---xSKTx--xFCUx---xSKTx
    makes no sense - the same would happen. The first FCU protects the connected sockets.

    That said. You need to look at what loads you are expecting to connect and where they are positioned on the ring. By design a leg on the ring (the cable between sockets) the Iz shouldn't go above 20A. If you are adding these sockets to either end of the ring, those closest to the CU - you could well do that. You need to calculate the leg length impedances for the final ring and calculate the expected current going both ways (parallel circuit). Someone qualified and with the correct test equipment can calculate these for you to make sure this would comply.
     
  7. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    I think I scared the OP off, by asking questions..
     
  8. Moley
    Offline

    Moley Baaaa!!!

    He posted at 4:56 am. Maybe posted before work or after night shift? So either he's just due home or just getting up?? I didn't even realise that time existed on a Sunday.
     
Loading...
Similar Threads - connect sockets fused Forum Date
10 amp inline connectors Electrical Forum Saturday at 6:14 PM
Domestic How to connect a single zone manifold into a multi-manifold system Underfloor Heating Forum Thursday at 8:41 PM

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job