best option would be a bigger CU. if you have. say. a 6 way, get a local spark to quote you for a 10/12 way dual RCD or RCBO board.Well, I guess that's true of many of us here. If I'm safe just to extend the radials ad nauseam then it looks like we're in business. I'll make sure there's a 20A MCB on each.
Note: In my own house (which is 500 years old and made of wood) I did the opposite to what you're suggesting. I inherited only two 32A rings for the whole place. I started by splitting these rings, junking the 32A MCBs, and converting them to four radials, each with a 16A RCBO.
Of course.I'm guessing you didn't have much loading on them.................. 20A RCBO's may have been a better approach!
Outdated?
If RFCs are outdated, what does that make Radials, which RFCs replaced?
It's not fashion week.
Ring finals are not outdated … rings are very versatile circuits, and where the building layout suits I still use rings when I need the 32A. Mainly kitchens and utilities these days. …
… The 32A 2.5mm^2 ring final has stood the test of time, and is far more flexible with installation methods.
… I don't like 32A 4mm^2 radials, the CCC is too close to the edge.
My main niggle with 32A rings is that a single point of failure (broken ring on one conductor - and surely every electrician has found this at some time) may result in a potentially dangerous cable overload which could sit undetected for years.
I have found plenty of non-continuous ring conductors. I have never discovered any thermal damage to cable due to overload caused by this lack of continuity though.
It's a potential hazard that exists only in theory in my experience. It would be interesting to see a bench test however and see how 2.5mm cable performs in this overload situation.
Wonder if JW has ever done this ?
Hmm. I don't entirely disagree, but to extrapolate your argument would be to say it's OK to protect buried 2.5mm T&E at 32A. Would you ever do that?
It would indeed be interesting to run, say, two old-skool 3kw fires down a long bit of 2.5 T&E to see what actually happens.
I would, and have installed 2.5mm cable protected by a 32A device. As a spur from a ring.
2 x 3kW fires on a bit of 2.5mm I would expect to be fine almost indefinitely with regards the cable. It is certainly just under the tabulated CCC of the cable.
If both were plugged into a double socket however, I would expect that to be the weak link as they are only rated at 20A.
Ha! Yes, correct of course, but you know that's not what I meant.
And sure, I once fused 0.5mm at 200A. For indicator lights in a main incomer switch panel. But I wouldn't use 0.5mm for 200A distribution, even if the budget was tight.
In the very specific case of a short spur or two, you are absolutely right in that the risk really is only theoretical, as no sensible person plugs two 3kW fires into the same double socket, or even in the same room. The radiated heat alone would set the curtains on fire before they needed to worry about the wiring.
My example was ill thought-out. How about a 3kW fire, a 1.5kW washing machine, a 1.5kW dishwasher, then a 1.5kW kettle on a broken long ring buried in insulation? Unlikely, but not impossible. And if it's said that such loads are very rare in practice, then why do we need 32A anyway?
I don't disagree that with quality modern cable, it would probably be OK for years. But I still say that any design which may need to take advantage of over-cautious specs and luck, is bad design!