Discuss Can somebody explain this. in the UK Electrical Forum area at ElectriciansForums.net

It's an attempt although flawed thinking to try stop flickering of lights or voltage drop probably from external sources, it not only would have little effect it is dangerous. I assume it was done as a joke tbh but there are idiots out there that may think this way.
 
That makes zero sense. When the MCBs are closed, the capacitors are approximately shorted out. When an MCB opens, a small amount of current leaks into the circuit from another circuit via the capacitor(s). The left hand one appears to be marked 10N which I read as 10nF. Current into a dead circuit would be 230.2.pi.50.10exp-9=0.7mA. The only application I can see is to suppress a breaker opening transient due to some odd stuff being on the circuit, but then you would want the suppressors all to a common point, not from one circuit to the next. Another possibility is that something radiates RF and the circuits are acting as antennas, being mutually isolated at RF by the inductive reactance of the magnetic tripping coils. The capacitors shunt the tripping coils paralleling the circuits at RF. All a bit far fetched. I think it's generally a mistake.

They seem to be polycarbonate dielectric types (no longer available) of about 630V rating (from their size). Not being self-healing like class X and Y caps, they are not intended for mains suppression applications and could fail short-circuit and prevent an MCB disconnecting the circuit.

Hmm, there might be something to what Darkwood says about a joke. Somebody might have been trying to teach their apprentice a lesson about isolation. Put the caps in to leak a small current into a circuit, enough to give them a jolt or a funny reading but not likely to cause serious shock. The value is about right for that. But then didn't take them out afterwards. Or left it as an easter-egg for someone else.
 
Agree with above. It is potentially dangerous and of no value that I can think of.
But for some reason it made me think of this sketch, and made me laugh, so I thank you Sham! You've given me a Capacitor and I'll raise you a Duck :) .
 
Some FM radio receivers used the mains lead as an aerial. A very low value class Y capacitor linked the Line to the tuner or there was a capacitive pick up by wrapping the wire FM antenna from the tuner several times around the outside of the mains lead. The idea being that frequency modulation would not suffer from mains borne interference as amplitude modulation would. Maybe then, whoever owned the home with this CU went a step further and combined at FM/VHF frequencies the final circuits for the sockets and internal lighting to form a much larger aerial array (and thus pick up a stronger signal) using these 10nF capacitors and relied on the mcbs' overcurrent coils providing high reactance to isolate it from the ground plane.

At 100MHz a 10nF has a reactance of less than 1 Ohm.
 
A little concerned that there are two 30A breakers with only one 2.5mm2 conductors then there are two 5A breakers which appear to have two 2.5mm2 conductors in one and three 2.5mm2 conductors in the other.
 

Reply to Can somebody explain this. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am buying a house and it was built in 1949. Is there anyway I can tell if it has tube wiring without opening up the walls? Is there anything...
Replies
1
Views
745
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
259
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
373
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
560
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock