Discuss Can you extend ring cabling with terminal strip inside socket back box? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
My boiler is currently plugged into a double 13A socket in my utility room. I want to move this connection to an FCU and add an extra double socket. As a general rule, I try to incorporate additional sockets and FCUs into the ring rather than via spurs, but the cabling that feeds the existing double socket is not long enough and replacing this cabling would require major disruption to the room above.

If I replace the existing socket back box with a deeper version, is there any issue with extending one of the ring cables via a 3-conductor terminal strip in the rear of the box?

Alternatively, is it OK to run a spur cable to the new FCU and then run a spur cable from the FCU to the new double socket?
 
My boiler is currently plugged into a double 13A socket in my utility room. I want to move this connection to an FCU and add an extra double socket. As a general rule, I try to incorporate additional sockets and FCUs into the ring rather than via spurs, but the cabling that feeds the existing double socket is not long enough and replacing this cabling would require major disruption to the room above. If I understand your proposal correctly.

If I replace the existing socket back box with a deeper version, is there any issue with extending one of the ring cables via a 3-conductor terminal strip in the rear of the box?

Alternatively, is it OK to run a spur cable to the new FCU and then run a spur cable from the FCU to the new double socket?
Providing the double socket you intend spurring from is part of the RFC and not a spur, of course the new 13Amp twin socket will be limited by the fact that the FCU will have a maximum 13 Amp cartridge fuse.
 
I would split the ring, one leg to the socket and the other to the spur, through crimp if necessary and install some 2.5 between the two outlets to maintain the ring.
 
Providing the double socket you intend spurring from is part of the RFC and not a spur, of course the new 13Amp twin socket will be limited by the fact that the FCU will have a maximum 13 Amp cartridge fuse.
What I meant was adding a spur to the new socket from the input side of the FCU. The fuse in the FCU would thus only protect the feed to the boiler.

I know you can't daisy chain multiple sockets via a spur, but I wasn't sure if you could do this with an FCU and a socket.
 
What I meant was adding a spur to the new socket from the input side of the FCU. The fuse in the FCU would thus only protect the feed to the boiler.

I know you can't daisy chain multiple sockets via a spur, but I wasn't sure if you could do this with an FCU and a socket.
Then No that would not be compliant
 
Westward10 has suggested using Wagos connectors, but I don't understand exactly what you mean by "through crimp".
Insulated Crimp Red Butt Pack of 100 - https://www.NoLinkingToThis/p/insulated-crimp-red-butt-pack-of-100/94616?kpid=94616&ds_rl=1245250&gclid=CjwKCAiA0IXQBRA2EiwAMODil719xAXNBgP5EdndUm8EBnGDCm7_nxxBLUg-DNb6ditRb6P5HcFXnxoC4gcQAvD_BwE&gclsrc=aw.ds&dclid=CJmJnuq6rNcCFSmN7QodkfMLZg
 
Insulated Crimp Red Butt Pack of 100 - https://www.NoLinkingToThis/p/insulated-crimp-red-butt-pack-of-100/94616?kpid=94616&ds_rl=1245250&gclid=CjwKCAiA0IXQBRA2EiwAMODil719xAXNBgP5EdndUm8EBnGDCm7_nxxBLUg-DNb6ditRb6P5HcFXnxoC4gcQAvD_BwE&gclsrc=aw.ds&dclid=CJmJnuq6rNcCFSmN7QodkfMLZg
That looks like quite a neat solution. I note that you have linked to a crimp that only takes 1.5mm2 wire and has a 19A rating (voltage rating is not quoted), but I guess that more suitable crimps are readily available.
 
That looks like quite a neat solution. I note that you have linked to a crimp that only takes 1.5mm2 wire and has a 19A rating (voltage rating is not quoted), but I guess that more suitable crimps are readily available.
Yes there are various types and sizes suggest you Google "electrical crimps " to view the range, please do not do as you suggested with the FSU and the twin socket outlet, which I described as non compliant.
 
Yes there are various types and sizes suggest you Google "electrical crimps " to view the range, please do not do as you suggested with the FSU and the twin socket outlet, which I described as non compliant.
My preference was always to incorporate the FCU and new socket into the ring, so I'm pleased that no one has an issue with extending the cable. The spur idea is now dead.
 
use push-in wagos or ideal butt connectors for your connection.

wago... upload_2017-11-7_13-11-8.jpeg

ideal butt connector.....
shopping
 

Reply to Can you extend ring cabling with terminal strip inside socket back box? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
631
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Hi, The walls have been chased out and he fitted 25mm back boxes and to be fair you can't really go any deeper but one socket on a ring is feeding...
Replies
48
Views
4K
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock