Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Can't find a reg on it, but it just seems wrong... in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Tags:
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Martyn Fletcher
    Offline

    Martyn Fletcher Regular EF Member

    Location:
    Essex
    Went to a job to check out a fault on an outhouse. Turns out that the outhouse is supplied via a 2.5mm T&E from the main house CU, which runs for several meters along an external wall (outside and unprotected) then disapears into a 50mm plastic pipe underground. The good bit is that at the other end (a post on which there is a metal box) the cable miraculously turns into a rubber 3core + earth.
    Now I know these cables are running in mechanical protection (no idea of depth) and I understand that there must be a joint somewhere along the route, but from a basic level is 2.5mm T&E running outside then going into buried conduit really compliant with regs?
    I can't find where it isn't but a seasoned Spark tells me it's not compliant.
    Any non sarcastic reply warmly welcomed. ;)
     
  2. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    What where the test results.

    You can’t mark down an installation because you don’t like the look of it!
     
    • Disagree Disagree x 1
    • Dumb Dumb x 1
  3. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    The external cable is not suitably protected from solar and mechanical damage.
     
    • Like Like x 4
    • Agree Agree x 3
  4. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    In fairness test results have nothing to do with his question as to whether it is a permissible installation method.
     
    • Agree Agree x 4
  5. Martyn Fletcher
    Offline

    Martyn Fletcher Regular EF Member

    Location:
    Essex
    I had an IR <30 Ohms between R1 and Rn and zero Ohms between R1 and R2.
    There was definitely evidence of degridation but that's not what I was asking.
     
  6. Dillb
    Offline

    Dillb Electrician's Arms

    Location:
    Nottingham
    Well those values are going to blow the OCPD arent they.
     
  7. davesparks
    Offline

    davesparks Forum Mentor

    Location:
    guildford
    The fact that degradation has occurred proves, in my opinion, that it doesn’t comply as an installation method.
    If nothing else the ref about good workmanship and materials etc hasn’t been complied with.
     
    • Like Like x 1
    • Agree Agree x 1
  8. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    True, but there are countless numbers of installations like these and even when picked up as issues on EICR’s owners don’t have to do anything about them ......
     
  9. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Apart from lack of UV protection (which could have been sorted with a lick of paint), there’s the hidden joint.
    Of course, if it’s an acceptable MF joint, then.....
     
  10. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    We were discussing the use of twin & e for outside in another thread, where @Pete999@Pete999 posted a video.
    It does appear that the OSG does suggest that it can be ok.

    upload_2018-7-10_22-25-38.png
     
    • Agree Agree x 1
  11. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Bobgeldof - so you’ve given me a dumb ..... what’s your opinion

    I’ve lost count of the amount of people that have ignored any comments or advice on improvements I have given.....
     
    • Like Like x 2
  12. Martyn Fletcher
    Offline

    Martyn Fletcher Regular EF Member

    Location:
    Essex
    OK! A bit of a filler for you... whole story.
    See picture below.
    The cable I mentioned above goes to a metal box on a post. From there it supplies an outhouse (as mentioned) and some stables some 40m away.
    The outhouse is subsequently fed witha 2core and Earth rubber cable which is jointed within the outhouse to a 2.5mm T&E (which also had faults).
    The stables were supplied from a cable I don't recall seeing before (see picture). It is a 20mm almost solid pvc cable with a solid core conductor. They had used one for the live and one for the neutral so there were two cables running the 40m to the stables. No earth and I haven't yet checked for an earth spike.[​IMG]
     
  13. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    That is their choice, as long as the Report is concise and accurate it is not your problem.
    It does not suggest it can be left exposed to the elements or mechanical stress.
     
    • Agree Agree x 1
  14. Martyn Fletcher
    Offline

    Martyn Fletcher Regular EF Member

    Location:
    Essex
     
  15. Marvo
    Offline

    Marvo Admin and gender confused Staff Member Admin

    Location:
    South Africa
    Yeah, nah...that looks maintenance free to me, as in it's not ever seen any maintenance.
     
    • Funny Funny x 7
Loading...
Similar Threads - Can't find seems Forum Date
Can't seem to find the answer, 18th edition tommorow ; ) Electrical Wiring, Theories and Regulations Feb 5, 2019
Can't figure out why it was done this way The Electricians Arms Feb 4, 2019

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job