Is TNS permitted on caravan site? I always thought you could use as TNS as supply cable then TT each pitch, spark I’m working with says you can use TNS all way through if ZS is acceptable
Thanks
 
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.

Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.
 
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.

Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.

ESQCR are does NOT allow pme conditions to a static caravan! It does allow it for buildings on parks, not the vans themselves
 
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.

Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.

If it is as you put it ‘A TN-S with PME conditions’ then it is not a TB-S is it?

It is up the the DNO to ensure their supply arrangement is vlear nit for us to go around asking questions.
 
Regardless, BS7671 is clear that a PME cannot be used.
No, it’s not.
From BS7671 Definitions:
Caravan. A trailer leisure accommodation vehicle, used for touring, designed to meet the requirements for the construction and use of road vehicles (see also definitions of Motor caravan and Leisure accommodation vehicle).
 

Reply to Caravan park Earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
848
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
538
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock