novernmunkee

hi guys can anyone help with this one
i have being given the task of maintaining emergency lighting to a large office complex.
the emergency lighting is fed of a ac/ac 230v central battery unit.
under normal conditions 230v flows through the cbu and out to the lighting, under fault condition i.e loss of 230v a bank of dc 110v batteries kick in which is then inverted 110v dc to 230v ac for a specified time
the problem i have is that how do i safely isolate the 110v dc batteries as i need to change them as they are on there way out
any suggestions greatly received and appreciated thanks neil
 
Before i will answer in any detail, What type of batteries are they, sealed maintenance free plastic, or the glass lead acid type that needs topping up from time to time?? How many batteries are we talking about here?? And what is the over all rating of the battery system??

By the way, this can be a very dangerous exercise, both disconnecting/removing the batteries and
installing/connecting them!!
 
Last edited by a moderator:
agreed im more affraid of batteries than i am of ac , a mate of mine dropped a spanner onto a bank of batteries and the spanner basically exploded

This is one area of work, where i would insist that all tools, including spanners and ratchet socket sets are 1000v insulated, ...Very little chance of that happening, dropping one of those spanners!! lol!!!
 
Last edited by a moderator:
I would just allow the emergency lights to drain the batteries.

The inverter will have a low battery voltage cut-off device, this will need disabling.

TBH it may be easier to just connect a load straight to the batteries and drain them completely.
 
Last edited by a moderator:
I would just allow the emergency lights to drain the batteries.

The inverter will have a low battery voltage cut-off device, this will need disabling.

TBH it may be easier to just connect a load straight to the batteries and drain them completely.

That's Bad advise!! This could cause a potential explosive build-up of gases/fumes within each battery cell, God forbid if you then accidentally short any +/- connections!!!

It could also damage the internals of the connected inverter trying to compensate for the lower incoming voltage..
 
That's Bad advise!! This could cause a potential explosive build-up of gases/fumes within each battery cell, God forbid if you then accidentally short any +/- connections!!!

It could also damage the internals of the connected inverter trying to compensate for the lower incoming voltage..

Totally agree with E54 not good advice at all.
 
he was alright just a bit shaken up, he said when he dropped the spanner his reactions made him look away thank god

I'm glad to hear he was ok. A good many years ago now I was installing Sub metering at a Milk Depot & was unfortunate to be present when an Engineer dropped a spanner across the Battery Terminals on an Electric Float. It's a sight & smell i'll never forget, the Guy lost 1 eye & part of his face. Possibly fortunately for him he died in Hospital a few days later.
 
1, Ensure batteries are totally isolated from their load. If they are passing current when you disconnect them, you will get arching. Depending on the battery type, this may cause explosions - especially if hydrogen involved.
2, Make sure area has been well ventilated to disperse any gases before battery disconnection.
3, Wear gloves, overalls and full face mask - electrolyte is very corrosive.
4, When disconnected, make sure you can easily lift batteries out for replacement.
5, Observe polarity for reconnection in same way. If batteries are connected in series banks, then be aware of potentially high DC voltages -nasty!!
6, With all new batteries in place and terminals tightly connected, you can then re-energise isolator.

Take care - banks of batteries can be very dangerous
 
I have to be honest and say if you've got no experience of working on large battery banks maybe get some assistance from a pro. Battery systems are very unforgiving and even a minor error can have spectacular results you really don't want to see. I've heard of several deaths of people from these systems.
 
I have to be honest and say if you've got no experience of working on large battery banks maybe get some assistance from a pro. Battery systems are very unforgiving and even a minor error can have spectacular results you really don't want to see. I've heard of several deaths of people from these systems.

Also, depending on the type and amount of batteries, the room they will be housed in, could well come under Ex rules. The ventilation and air exchanges requirements could also come under other explosion-proof room regulations, along with sophisticated gas detection fire alarm system. Battery storage bank rooms can be a very dangerous environment when things start going wrong!!

Almost all of the major project's i've been involved with, have all had such installations for the uninterruptible DC supply related to the main MV/LV switchboards control circuitry generally 110 V/DC...
 
Well remembered E54 i'd forgotten about EX requirements for Battery rooms, shows how long ago I last did 1. Beginning to feel old now:lol::wheelchair:
 
thanks for all the advice guys much appreciated i'll get as much information as i possably can from the batteries cbu before i proceed any further
 
Have a look at

http://www.sonnenschein.org/PDF files/BatteryRoomVentilationInstallation.PDF

I’ll be honest I hate working on large battery systems. If I have to then I split the banks in to small units of say 30V each.

One thing to bear in mind is why they are there. You can’t start messing about with critical systems without forward planning.
I’ll quote an engineering manager “swap over to the new battery bank while the plants are running”. My reply would soon get censured by Marvo! I did the change over at midnight on a Sunday when I could safely shut down the 40MVA 11KV board. Any fault while I was doing the change over wouldn’t clear until the batteries were reconnected.
 
Last edited by a moderator:
My reply would soon get censured by Marvo!

You're probably right, I would also have had a few choice words :)

Large battery installations were a part of my apprenticeship but I still avoid them like the plague. It's just an environment I don't work in very often and I'm not that comfortable in. I also know how dangerous they can be.
 
Just read this PDF file, and while i can agree with most of what's been written/stated, i can't reconcile the statement about ''Must Not be Ex protected'' Every battery room installation i've been involved with has been fitted with Ex lighting fittings and lighting switches (where switches were located in the room). All conduit and fittings were PVC covered heavy gauge apart from the light fittings and switches, and with sealing adaptors . Main Battery isolator was again Ex, and mounted on insulated metal floor bolted frame. Battery racks were positioned in the centre of the room to allow free air flow through the battery rack

The room walls were tiled using epoxy grout, the ceilings and floors were sealed and coated with an epoxy paint!! No ventilation fans permitted to be located within the rooms boundary, eg ducted supply and extract!! Extract ducting incorporating gas detection sensor and optical smoky... Rooms had halon gas (and now halon replacement) mass discharge suppression system.

So as you see, a bit different to what has been stated in this PDF file. All i can think of, is that our specification(s) are based on a standard(s) other than the EN 50272-2, referred to in this file data??? Can't help thinking that, not all information was being being given in the file either....



http://www.sonnenschein.org/PDF file...stallation.PDF
 
Last edited by a moderator:
To be honest E54 I’ve never done a battery room install, but I’ve inherited them as existing. I don’t think I’ve ever seen two similar set ups. Some I will say were death traps but the companies were unwilling to spend anything, the usual “it’s been like that for the last XX years”. Give up it’s the less painful option unfortunately became the norm.
 

Reply to central battery unit in the Australia area at ElectriciansForums.net

Similar Threads

I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
585
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
Hi. Can someone let me know if this is right? I have a Led light which has emergency battery backup. Trying to figure out if what I have worked...
Replies
1
Views
2K
I have an interesting job/project coming up - a heritage railway has a Mk3 Sleeper Railway Carriage which they intend to use for volunteer...
Replies
30
Views
3K
Hello, this emergency light does not come on when power is cut. There is a red light on when house has power, indicating power to the unit. The...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock