Discuss Choosing the right size cable in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
1
Hope someone can clear something up for me.
I've been selecting cable recently to wire up industrial machinery for test purposes only.

I usually purchase H07RN-F or H07BN4-F.

My boss has informed me that the cable needs to have a current carrying capacity to match the supply it's being being connected to. For example if the equipment is being connected to a 415v 32a supply the cable in the case of the H07RN-F needs to be 6mm irrespective of the load.
Say the load is known to only draw 3A I have been selecting lower CSA cable based on the load requirements of the equipment but he says that if I do this the cable should be protected by a suitable breaker.

I do a fair bit of pat testing and often see equipment with 2.5mm h07 cable connected to equipment which has a 32a plug fitted.

Is he getting mixed up with installation cable selection as opposed to selecting suitable cable for equipment.

If I'm making an extension lead I always use 6mm cable as It should be capable of carrying the full 32a as I don't know what will be connected to it.

Are there any books I can read on equipment wiring.

Sorry for the long question just really would like to clear it up.
 
you select your cable according to the load current. then select your MCB/fuse according to Ib<In<Iz. pointles installing a 32A cable for a 5A load, but then the MCB rating must be below the max. ccc of the selected cable. e.g. if the cable will take 20A max, then the MCB In must be < 20A
 
Haha thanks guys.
The problem is I can't change the size of the MCB in the distribution board which will be rated at the full 32A as the sockets are used by all and sundry on the shop floor for all sorts of applications tool use etc.
Thats what he says, the cable should be capable of carrying the full 32A under fault conditions.

But this doesnt seem practical to me I know I have a water chiller in my workshop that only draws a few amps and is fitted with 2.5mm cable and a 32A plug are you saying that this should be protected with a 20 MCB in the panel ?
 
Thats what he says, the cable should be capable of carrying the full 32A under fault conditions.
Then I would hazard a guess that he doesn't know a lot about fault currents and circuit design as a fault current would be a lot higher than 32 amps (TT system excepted).
 
Then I would hazard a guess that he doesn't know a lot about fault currents and circuit design as a fault current would be a lot higher than 32 amps (TT system excepted).
He's a very experienced electrician who I have alot of respect for I guess what he's getting at is that providing the cable is big enough to carry 32A under fault conditions the breaker would trip before the cable melted
 
How do you know there will be no risk of overload?
I can understand a motor may be worked too hard and draw more than the FLC but this wouldn't apply to everthing
Under normal conditions many appliances with a fixed load will not draw a higher load than their rating.

For example (Extreme example for those lurkers that may decide to google lighting circuit designs and actually think something on the internet is true...) a 100 watt lamp will not draw more than 100 watts so in theory you could supply the lamp using 1mm cable fed from a 32 OCPD. When you start to add more lamps then you need to consider the cable rating in relation to the OCPD.
 
How do you know there will be no risk of overload?
I can understand a motor may be worked too hard and draw more than the FLC but this wouldn't apply to everthing
This is one of those risks I hinted at - risk of not knowing everything. If the load was a heating element say, then it really can't do anything other than open circuit, normal load current or fault current (limited by Zs).
 
Ok thanks for your advice.

On a side not it's much easier selecting the cables from our control panels to the motors and the other equipment they control as the devices do then have suitable breakers and adjustable overloads.

Ah well I'm learning all the time by the time I retire I may be getting somewhere
 
But this doesnt seem practical to me I know I have a water chiller in my workshop that only draws a few amps and is fitted with 2.5mm cable and a 32A plug are you saying that this should be protected with a 20 MCB in the panel ?

Then the water cooler has the wrong plug on it, it would be better on a 16A plug as that is the smallest commonly available size of 3phase plug and socket.
The water cooler would hopefully also have its own protection for the appliance, mcbs are there to protect the cable, not normally the appliances.
 
Then the water cooler has the wrong plug on it, it would be better on a 16A plug as that is the smallest commonly available size of 3phase plug and socket.
The water cooler would hopefully also have its own protection for the appliance, mcbs are there to protect the cable, not normally the appliances.
Ok that makes sense apart from we have have no 16A outlets on the shop floor.
The place is slowly being upgraded a bit at a time but I don't think I will be getting and 16A sockets in the near future.
 
Ok that makes sense apart from we have have no 16A outlets on the shop floor.
The place is slowly being upgraded a bit at a time but I don't think I will be getting and 16A sockets in the near future.

The fact that you don't have any suitable sockets available doesn't change the regulations or magically make the dangers vanish.
Suitable equipment to safely adapt a 32A outlet down to 16A is available from people such as the rubber box company.
 
The fact that you don't have any suitable sockets available doesn't change the regulations or magically make the dangers vanish.
Suitable equipment to safely adapt a 32A outlet down to 16A is available from people such as the rubber box company.
I appreciate that and your advice hence why im trying to get an better understanding on best practices.
Its just the contradictions I come across which confuse me.
For instance with the 110v equipment like drills and grinders they are sometimes fitted with cable suitable for the load only and not 16A
 

Reply to Choosing the right size cable in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
21
Views
569
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
604
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
558
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock