desertbootz

Taking over a building and starting to get PIR's for handover. They are NICEIC styley and under Circuit Impedence they have three columns for Ring and two for 'All Circuits'. The tester has filled in all columns for every cct but they don't make much sense, eg, 4mm line and cpc, R1=0.39, Rn=0.42, r2=0.50 which seems okay (allowing for meter error etc.) but then the 'All Circuits' column shows; R1+R2=0.14, R2=0.50.

How do you get an R1+R2 lower than the values of R1 and R2? Is he bluffing it or am I being a mong?

All advice/abuse received in the manner it's meant :O)
 
hi i get r1+r2=0.22
the first readings he gives are r1 end to end the same for r2 and rn
with the r1 and r2 cross linked the reading at the sockets should be approx 1/4
r1+r2/4
 
Maybe I wasn't clear. I understand R1+R2 on the ring is measuring the conductors in parallel hence the lower reading but how/why would these readings be filled in for lights?
 
We should not assume the lights are radial
There are occasions for example, volt drop problems, where ring circuits for lights are installed
What does it say in the column for number of conductors for the circuit
(if the nic form has this column)
 

Reply to Circuit Impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in...
Replies
30
Views
4K
P
Hi all, I am hoping someone can clarify if my understanding on earth fault loop impedance testing is correct. A low efli is needed so a...
Replies
8
Views
2K
Hi guys, I have come across two problems today well acutely three so I will list them first.. 1st Testing a 4mm radial circuit today or so I...
Replies
18
Views
7K
Engineer54
E
S
Anyone got any ideas? Measured R1, Rn, R2 end to end and 0.34, 0.35 and 5.6 ohm. Measured R1, R2 crossed and got between 0.21 and 0.23 ohm at...
Replies
4
Views
1K
sbelec
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock