Story is i got called to finish off the heating on a new build as the electrician doing the work was too busy to get back in time.

There were some cables run, and some equipment fitted, and ive done the rest. There is no diagrams.. ive had to google what I can.

Its an S plan system, 2 motorised valves, 2 channel programmer and the tank stat and room stat. The boiler is a Worcester Greenstar 18i System boiler

Permanent supply to boiler, in turn feeding the programmer and both valves.
Switched feeds from the programmer back to the joint box, connected to the tank stat and room stat. These in turn operate the valves, when fully open send another feed to the boiler to tell it to fire up.

Part of the confusion was that the heating engineer had installed a pump on the pipework, where the boiler has an integral pump... so that had to come out.

Everything works as it should up to where the valves tell the boiler to come on. The switch wires from the valves are connected in the boiler to LR with a radiator icon, and LR with a tap icon.
What I think, reading through the 18i installation manual is the 2 valve switch wires are joined together and both connected to LR with radiator... LR with tap has nothing connected to it.

Does that sound familiar to anyone?

(The two LR connections were already connected in the boiler by the previous electrician)
 
Use LR heating (radiator symbol) to fire the boiler.
Don't connect anything to LR hot water (tap symbol) this is only used when an integral diverter valve is used and doesn't do anything when this is not fitted.
 
The other pump doesn't have to come out and can be connected to the oranges of the valves. There should be a link between L and LR tap. And connect oranges of the valves to LR radiator.

But if theres two pumps, coming on at different times (one from the valve, one from the boilers electronics) the water wont flow against a stopped pump? I don't know, but surely it's not needed.
 
But if theres two pumps, coming on at different times (one from the valve, one from the boilers electronics) the water wont flow against a stopped pump? I don't know, but surely it's not needed.

You're right ugh the it's not needed, but if it's there then it can be connected to the S/l to the boiler.
The second pump will always run when the valves are open that way, and when the valves are closed then the stopped pump won't make any difference as the water won't be able to flow through the valves anyway. At this point the boiler pump will be pumping through the bypass fitted to the pipework.
 

Reply to Clarification of CH wiring (no diagrams!) in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
903
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
585
Anyone tell me where to connect the two wires that switch the boiler on via the programmer and the 2 wires that call for heat on the ufh control...
Replies
1
Views
247

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock