I'm sure this has been asked before, and I have done some searching here, but not quite sure how to phrase it to search properly.

I have just completed some minor works on a property installed to the 16th, i.e. no rcd's on lighting. The client required replacement of existing ensuite lighting, like for like (to Zone 1 fittings). I checked with Elecsa, to make sure this was acceptable. There was supplementary bonding in the ensuite bathroom, although there was non evident in the water heater/imersion cupboard, although the continuity readings were low (decided to cross bond here anyway).

My question is how to complete the Minor Works Cert. Part 1, sec 'Departures from BS7671 2008'. How do I complete this section in the above circumstances?
 
My question is how to complete the Minor Works Cert. Part 1, sec 'Departures from BS7671 2008'. How do I complete this section in the above circumstances?

If you are issuing a MWC then you would complete the departures section as "none". You are still complying with BS7671.

However you should note in the comments on existing installation that there is no RCD protection to the existing lighting circuit, but there is existing supplementary bonding in the bathroom and the supplementary bonding has been installed in the immersion cupboard.
 
In line with what Mr Burns states you are only responsible for ensuring the work you complete is compliant with BS7671. If it wasnt then you would complete the departures section with the non-compliance you are installing complete with reasons for doing so. To the best of my knowledge I cant think of any legitimate reason why you could undertake work not compliant with BS7671 so this section should always be 'NONE'.

If there are any irregularities with the installation c.f. current BS7671 requirements then highlight these in the comments section. If for no other reason than to cover your 'butt' should something untoward happen at a later date due to the non-conformance!
 
Thanks chaps. Only recently completed my first assessment, so certain bits of the certificates confuse me, but I understand this part now - None it is. I thought I would do a MWC to cover myself, but isn't notfiable - all work in a special location, even just changing a fitting? All though I suppose that would prevent householders from ever doing simple tasks themselves.
 
would be notifiable only if you altered the characteristics of the circuit, or installed a new circuit.
 

Reply to Clarification on Minor Works Certification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Interesting situation has come up. I have a client who rents out portable toilets - higher end ones with proper flushing toilets/urinals that are...
Replies
7
Views
3K
Good evening, A burning question has arisen in my mind regarding minor works certificates. This is, if you do some work for a customer which...
Replies
8
Views
1K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
There are lots of discussions on forums about what is and isn’t Part P notifiable work. Everything I have done on the past or would want to do in...
Replies
6
Views
7K
Deleted member 26818
D
Hi folks, this will probably be obvious to most folks on here but I'm new to this. A friend is putting together a quote to rewire my house. He is...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock