Fault on micc, one leg of two-core down to earth.

Anyhow big probs cos fixed / glanded into conduit box in concrete ceiling...supposed to be phased and tested before, the fault magically appeared after!

Ideas what to do and get out of hole before boss finds out

We settled on one guys idea who had done it before and worked...

wang 240v down it on 30A rewirable it may clear...

.....yep blew the pot out of the ceiling!

Just talked to him on phone, have to laugh about it now

So if any of you guys are faced with the same prob, try a 5A first -;
 
There's down to Earth and there is low reading!!!

Low reading is a sign of a little dampness and yes it as been known for "sparks" to liven up a MICC to dry it out. This is a quick fix and to be honest not a particularly good one as often as not dampness will get into the pot again and breakdown the sealant and do exactly what happened to your pot.

The liven up the circuit really was a "good enough for the country" job, and let someone a few months down the line worry about exploding pots.

This though would not work on a fully down to earth
 
sure did tony, except nothing left to connect anything to.

The gaffer wern't too pleased but said run another leg surface, there's a suspended ceiling going in here....nobheads
 
This though would not work on a fully down to earth

I would argue it could and has worked before, a hairline fault would blow before the 30A rewirable fuse
 
Fault on micc, one leg of two-core down to earth.

Anyhow big probs cos fixed / glanded into conduit box in concrete ceiling...supposed to be phased and tested before, the fault magically appeared after!

Ideas what to do and get out of hole before boss finds out

We settled on one guys idea who had done it before and worked...

wang 240v down it on 30A rewirable it may clear...

.....yep blew the pot out of the ceiling!

Just talked to him on phone, have to laugh about it now

So if any of you guys are faced with the same prob, try a 5A first -;



The times i've heard this gem of a solution to clear a MICC pot earth fault!! All it will do at best is leave a carbon deposit from the pot to the conductor by the fault flash.

I'm afraid the only way to correct, is to chop out the concrete from around the Besa box to release it, and around 6'' along the route of the cable to allow you to remake the pot, then repair the area when all back in place. A real pain of a job, and why you ALWAYS check and double check any made off lengths of MICC cable, BEFORE it's embedded in the fabric of the building.
 
Fault on micc, one leg of two-core down to earth.

Anyhow big probs cos fixed / glanded into conduit box in concrete ceiling...supposed to be phased and tested before, the fault magically appeared after!

Ideas what to do and get out of hole before boss finds out

We settled on one guys idea who had done it before and worked...

wang 240v down it on 30A rewirable it may clear...

.....yep blew the pot out of the ceiling!

Just talked to him on phone, have to laugh about it now

So if any of you guys are faced with the same prob, try a 5A first -;

As I said in the post if it was dampness then you may have cleared it.

But no matter what you do with a full earth fault it will not clear, it will either blow the pot or the fuse

I thought you were trying to clear it as you stated in your OP, you will never clear a full earth fault.
 
And by the sheer nature of an explosion, carbon flash points may or may not leave direct conductive paths.

I have been assured it can work, by a trusted and yes alright eccentric sparks
 
malc, i did state we were attempting to clear it, it didn't work on this occaision. We were aware of damp, this was a dead short.
I ought to have stated, sorry
 
And by the sheer nature of an explosion, carbon flash points may or may not leave direct conductive paths.

I have been assured it can work, by a trusted and yes alright eccentric sparks

Rather you than me, this would be the very last thing i would attempt. The chances of that fault flash leaving a conductive path between the conductor/ pot / sheath is a dam sight higher than it not!! Even if the conductive path is minimal, it will create a permanent weakness in this lighting circuit. One that i certainly wouldn't be happy about walking away from!!!
 
For qualified only:
Assuming rewirable fuses, you can easily test the theory behind
Split a length of .75mm flex, take out one strand (I have no idea what size this would be, but would guess arround 0.075mm)
Turn off power
Take off socket front and connect strand between line and earth. If you want you could surround the connections with compound to replicate an micc termination.
(If tested this would show a dead short)

Turn on power
The strand will blow (assuming earthing is up to spec.)
The rewirable fuse may also blow, replace rewirable fusewire, and reconnect to supply.
You will see no fault, although you may or may not see a low reading
Of course not to be attempted by diy
 
For qualified only:
Assuming rewirable fuses, you can easily test the theory behind
Split a length of .75mm flex, take out one strand (I have no idea what size this would be, but would guess arround 0.075mm)
Turn off power
Take off socket front and connect strand between line and earth. If you want you could surround the connections with compound to replicate an micc termination.
(If tested this would show a dead short)

Turn on power
The strand will blow (assuming earthing is up to spec.)
The rewirable fuse may also blow, replace rewirable fusewire, and reconnect to supply.
You will see no fault, although you may or may not see a low reading
Of course not to be attempted by diy


Are you actually being serious here??




Why? If a fault it will trip, if not it won't?


It could well do, but at a latter date, it then may never re-set, so leaving the original fault with this circuit, for some other poor bugger to fix!! Brilliant!!!

So why not correct this MICC fault using a proven conventional means, and not trying to bodge your way through it??
 
Last edited by a moderator:
Bodge? If its clear, its clear...or maybe you know down the line all clear always clear?

Are you paul daniels?

I've been in this game long enough to know that little statement can come back and bite you in the arse, especially when talking about MICC pot faults. Blowing an earth fault apart in a MICC pot that you can't inspect is NOT a good idea ...Full Stop!!!

And you don't have to be a Paul Daniels or a clairvoyant to know that!!
 
I have in the distant past removed pots to check. IR test still showing phase to earth fault. I was shown a trick that has worked on several occasions especially if the Pot has been twisted slightly when gland was tightened, give the conductors a pull with a pair of pliers directly inline with the MICC to pull them straight IR test again and bingo fault gone (sometimes) Fit new pot fill with compound and retest.
 

Reply to clearing fault on micc in the Australia area at ElectriciansForums.net

Similar Threads

Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
A
Hi guys I’m new to this site however just thought I’d give my best explanation of what the AM2 was like. If this is in the wrong forum I’m very...
Replies
29
Views
11K
I got called out to house a few days ago with the main rcd tripping when they turned the hot tap on with the combi firing up.They had only just...
Replies
8
Views
22K
hello. just wondered if any of you have experienced this or can possibly shed some light on it. today i went to a fault on an immersion circuit...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock