Recent EICR at a special needs care site found a built in double oven (4.2kw) connected to a 4.0mm ring final on a 30a C50 mcb. Two other double sockets on the ring for general use and an FCU for a fridge. Interested in what code people might apply to that, no need to consider RCD or anything else, only interested in the above issue. I'll keep mum on how I coded it until some other opinions come in!
 
C3 IMO. although not ideal, I can't see a potential danger as any overload would trip the MCB before the cable was compromised. or was it on a BS1363? in which case I'd lean towards a C2 (plug/socket overload and overheating).
 
A bit of a puzzle ... RFC from 4mm doesn't have a text book rating (that I recall) but it does not sound overloaded. Sorry feeling dense this morning, is it a 50A C type mcb? If circuit can make dis times then C3.
 
I would agree with Tel on the C3, it is borderline no code.
Generally heavy consistent loads should not be placed on a ring final because of the potential to overload one leg of the ring. However an oven is not a consistent load, although 18A is fairly heavy for a single point on a ring, with 4mm² conductors one leg of the ring cannot be overloaded even with a type 2/type C hydraulic MCB @ 30A.
Assuming all other factors remain compliant I cannot see it giving rise to danger but I can see it possibly tripping the circuit breaker but no more than with any socket circuit really as there are only four (six) points of use, unless the general use sockets are often used for heating loads by the nature of the installation.
I am probably pushing the justification for a C3 but feel that even an 18A oven should be on its own circuit so would recommend improvement from a design rather than a danger point of view.
 
I would agree with Tel on the C3, it is borderline no code.
Generally heavy consistent loads should not be placed on a ring final because of the potential to overload one leg of the ring. However an oven is not a consistent load, although 18A is fairly heavy for a single point on a ring, with 4mm² conductors one leg of the ring cannot be overloaded even with a type 2/type C hydraulic MCB @ 30A.
Assuming all other factors remain compliant I cannot see it giving rise to danger but I can see it possibly tripping the circuit breaker but no more than with any socket circuit really as there are only four (six) points of use, unless the general use sockets are often used for heating loads by the nature of the installation.
I am probably pushing the justification for a C3 but feel that even an 18A oven should be on its own circuit so would recommend improvement from a design rather than a danger point of view.



I agree the thing that would lead me to a code ; providing the oven connection is sound - given that is is a care home and the oven will be used throught the day in my experience .
 
Agree borderline C3 - unless the installation method seriously reduces the CCC of the 4.0, and subject to the connection being effectively made

is it a 50A C type mcb
C50 is the old Crabtree MCB board model number, with tbe brown bakelite BS3871 MCBs. Hence 30A not 32A and type 2/3 not B/C.
 
Agree borderline C3 - unless the installation method seriously reduces the CCC of the 4.0, and subject to the connection being effectively made


C50 is the old Crabtree MCB board model number, with tbe brown bakelite BS3871 MCBs. Hence 30A not 32A and type 2/3 not B/C.
Crabtree C50 are either 3871 type 2 or 3871 type C. Recent new styles which are now discontinued were 60898 type C. If there is no identification on the side except BS3871, assume type C. There was never a type 3.
 
Interesting, it's a while since I spent any real time amongst C50 boards and I'm not sure I even realised that in the first place.
 
Interesting, it's a while since I spent any real time amongst C50 boards and I'm not sure I even realised that in the first place.
Somewhere amongst my junk I have a fax from Crabtree with all the info, have only ever seen one 60898/C in use though.
 
Thanks for that everyone. I applied a code 3 really just to highlight an unusual installation, I can see no danger or risk of overloading as it stands. There was a discussion over this between the site and another electrician following the issue of the report who stated it was unsafe and should have been a code 2.
The breaker is a non type marked crabtree C50 30a 3871 M3 (white lettering). For the purpose of Zs I assumed type C as worst case, as long as the Zs was under the max for that it would be under for other possible types. That was explained on the report.
 

Reply to Code 2 or 3? Opinions please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock