    As it says - what code should I be giving to a metal CU where the cables come straight in through the knockouts without any form of protection. Meter tails and main earth enter through different apertures 'n all.
     
    • Like Like x 1
  2. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    C2 in my book. no cable restraint and chance of shorting out to CU casing. potential dangerous. the different holes i'd code as C3 as the small eddy currents on a dom. will not cause a problem
     
    • Agree Agree x 1
  3. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Are the tails insulated and sheathed?
    Is there any signs of damage /abrasions to the tails?
    And is it TT?
     
  4. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You sure you should be doing EICRs.
     
    • Like Like x 1
    • Dislike Dislike x 1
  5. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Whilst I agree that in reality it's unlikely to pose any real issue in a domestic installation I would still C2 it as it is not something which I would condone.
     
    • Agree Agree x 1
  6. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    C
    C2 potentially dangerous?
    If there was evidence of thermal effects on the enclosure then that's the only time I would C2 it for tails entering different holes.
    Just my opinion tho.
    I'd be more concerned with the lack of protection to the cables entering the enclosure.
     
  7. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Is the main earth a"tail" ?
     
    • Agree Agree x 1
  8. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    It does have the potential to be dangerous, although as stated with the loads in a domestic installation this is unlikely.
     
  9. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    The earthing conductor must pass through the ferromagnetic enclosure together with the live tails. I'm not sure if that was what you were asking though.
     
  10. solarsavings
    Offline

    solarsavings Electrician's Arms

    Location:
    Cambridgeshire
    I think this one is c1.
    Done 3 months ago.
    No paperwork.

    Den 1.jpg

    Den 2.jpg

    Den 3.jpg
     
    • Disagree Disagree x 1
  11. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Yet a seperate cpc can enter a separate hole if ran in parallel with a swa
     
  12. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
  13. solarsavings
    Offline

    solarsavings Electrician's Arms

    Location:
    Cambridgeshire
    Went there today following a report of downstairs not working. She paid him £350 cash
    for that.
     
  14. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    There's no eddy current issue for me
    Oh wait those photos are a different job unrelated
     
  15. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    TN S. No signs of damage. I'm not doing an EICR just installing outdoor lighting.
     
  16. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    • Agree Agree x 1
  17. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    you asked what code ?
     
    • Agree Agree x 1
  18. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    For the 7671 cert. They've got like a mini EICR on them now.
     
  19. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    What do you think would warrant a C1?

    Which certs are you using? The ones in BS 7671 don't have a check list!
     
  20. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Only recently - it was prohibited until a handful of years ago.
     
  21. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    C1 for no blanks - Direct access to live parts.
     
    • Agree Agree x 2
    • Like Like x 1
  22. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Presumably the missing blanks giving access to live parts.
     
    • Like Like x 1
    • Agree Agree x 1
  23. uksrevivor
    Offline

    uksrevivor Trainee Access

    Location:
    South Wales
    Access to live parts a major issue on that installation by not fitting blanks, Knockouts with no glands and tails showing signs of damage. Tail gland kits are not expensive and make such a neater looking job. The MET appears to have a 16mm from DNO cut out to MET block then a 10mm run into the consumer unit, also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water? the lack of labeling on the CU and MET also shows signs of a cowboy installer grab the cash and run jobby to me.
     
  24. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    also there is only 1 10mm bonding cable from MET block which would mean only 1 bonding cable running to incoming gas or water

    Or even to both via one cable ;)
     
    • Agree Agree x 1
  25. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Which doesn't even have to be continuous.... but is good practice to be a single cable
     
    • Agree Agree x 2
  26. uksrevivor
    Offline

    uksrevivor Trainee Access

    Location:
    South Wales
    I was taught to run 1 to water and another to the gas from the MET.
     
  27. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    Then your teacher was correct,both services sometimes require bonding, running a cable to each can cover that requirement
    there is however,more than one way to skin a cat :) and because something is done correctly,it does not mean there are not other permitted means to comply

    Quite a lot of electrical requirements can be achieved with differing solutions, it can be elusive sometimes finding justification for another persons method

    I suppose that is why electricians are regularly disputing or interpreting regs with one and other,they can have differing and compliant means to reach the same outcome
     
    • Like Like x 2
    • Agree Agree x 1
  28. uksrevivor
    Offline

    uksrevivor Trainee Access

    Location:
    South Wales
    Exactly why i love this trade i learn new ways all the time. My boss would always want me to install separate bonding to incoming gas and water and thats what he prices for so i do as he says, but every spark is different and as i say im learning all the time and loving it.
     
  29. Paul228
    Offline

    Paul228 There is no spoon

    Location:
    Hull in Yorkshire
    Standard finger -if you can poke something 12.5mm in dia and 75mm long and touch and exposed part then it needs to have a gromit/ gland fitted.
    I remember my collage lecturer finding a standard finger amusing. I don't know why?:rolleyes:
     
  30. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    The tutor was a female ?
     
  31. Paul228
    Offline

    Paul228 There is no spoon

    Location:
    Hull in Yorkshire
    Unfortunately not. A 60 yo, 17stone guy with a ZZ top beard.
    I might of paid more attention if he was a she
     
    • Like Like x 1
Loading...
Similar Threads - Code lack grommets Forum Date
Code 2 or 3? Opinions please. Electrical Forum Saturday at 9:22 AM
Loop Impedance Testing - Strange fault code Electrical Tools and Products Aug 23, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job