Can anyone confirm the one meter rule from the external edge of the roof. i.e. what is the EDGE?

Is this from the panels to the ridge? i am assuming the edge is the sides and at the eaves.

I'm thinking the ridge is not the edge but confirmation would be appreciated.

Thanks

"the solar PV or solar thermal equipment would be installed on a roof and within 1 metre of the external edge of that roof;"


 
Devon planning do not decide the law they have to interpret it - correctly.

The relevant part of SI 748/2012 is the Schedule Part 43 Class A Clause A.1.(c)

"...the solar PV or solar thermal equipment would be installed on a roof and within 1
metre of the external edge of that roof;"

I would read it in the normal english use of the words 'external edge".

So I would definitely say a ridge within the plan area of a roof is NOT an external edge.

Eaves on the outside of the building are definitely an external edge.

Up for debate is whether internally facing eaves on an internal courtyard count as an external edge of the roof. I suspect planners might be reluctant to push the point if that were the only issue.
 
We are based in Exeter and have found the planning dept. very helpful. They interpreted the external edge as eaves and any applicable gable ends. They weren't concerned about the ridge unless the highest point of the system protruded higher than the highest part of the existing structure (eg the ridge) or 200mm from the roof plane (the same as domestic PV systems).

Hope this helps?
 

Reply to Commercial permitted development - confirmation required in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
124
Hi, Recently I had solar panels fitted and realised how they have done it and I hope someone will be able to give me advice how bad and dangrous...
Replies
16
Views
3K
We have solar PV panels (1.5kw) and I'm curious about fitting an immersion diverter to use any spare solar energy for heating water rather than...
Replies
3
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
540

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock