I've treated myself to the IET Electrical Installation Design guide. I've been looking at section 3.5 Complex Installations. There is a calculation for calculating demand based on number of dwellings in a group.
Please see picture of relevant page.
Seems simple, sub domain is 66.44A, demand factor (g) for 8 dwellings is 0.22
The calculation is therefore 66.44 + 0.22(8 -1)66.44 = 168.76A
So my question is what do I need to type into the calculator to get the magic answer of 168.76A ?
s!ApQQCRGg1ka_gv4PRpTYjGK5EMA17w

As a side note can you see the image okay?
 
Hi Michael - not sure I understand correctly as the equation in OP equals 168.76A ... but you have that already (?) . I can see the pic now, so I'll take a closer look at it.
 
I've treated myself to the IET Electrical Installation Design guide. I've been looking at section 3.5 Complex Installations. There is a calculation for calculating demand based on number of dwellings in a group.
Please see picture of relevant page.
Seems simple, sub domain is 66.44A, demand factor (g) for 8 dwellings is 0.22
The calculation is therefore 66.44 + 0.22(8 -1)66.44 = 168.76A
So my question is what do I need to type into the calculator to get the magic answer of 168.76A ?
s!ApQQCRGg1ka_gv4PRpTYjGK5EMA17w
max demandhttp://www.napitonline.com/downloads/CP%204%2007%20P%2010-11%2016th%20Diversity.pdf
 
Looks like a misprint to be honest.
Factor g is usually a multiplier for diversity so wouldn't make sense to add it. This seems to get you to the printed answer though

(66.44*0.22)*(8-1)+66.44

Workings:
66.44*0.22 = 14.6168
14.6168*(8-1) = 102.3176
102.376+66.44 = 168.76

I would send the IET an email asking for clarification. Could be a misprint or you could have a counterfeit copy.
 
Andy is correct and it is a misprint as I have the same book.
In fact there’s several mistakes in it such as giving the max zs of a type b 32 amp mcb as 1.44 ohms then directly underneath or above this example it gives the correct figure of 1.37 ohms.
Also uses old reference methods such as reference method 1 and reference method 3 etc.
Still a decent book tho.
 
66.44 + 0.22(8 -1)66.44

That isn't a misprint in the mathematical sense... it translates to:-

66.44 + (0.22 x 7 x 66.44) which does indeed equal 168.76A

If the values are wrong that's a different matter but mathematically it is correct.

Now I'm admittedly not the best at maths and never have been but that just confuses me.
The way it is written in the book does not equate to the way you have written it in your third line in my mind. Help a guy out to understand that ?
 
My 11 year old daughter has just taught me about BODMAS. Brackets, Orders, Divide, Multiply, Add, Sub
I now agree with Sparkychick,

My 12 year old sons have just taught me their version, BIDMAS, which also now makes sense. Some things I just never grasped. Don't think I'm wired the right way.

Not as bad as when they got given long division problems at age 9 and I had to teach myself it for the first time to be able to help them. What a week that was !
 
It's about the order of evaluation and some basic algebra.

If you have A=2 and B=3... AB=6. This is an implied multiplication. And is either not shown as an operator or is shown as "x" or in the modern age "*".

So A x B, A * B and AB are mathematically identical, all giving the value 6. The order of evaluation is as @Michaelwgroves has stated... Brackets, Orders, Divide, Multiply, Add, Sub

For the most part, divide and multiply are interchangable as are add and subtract.

So using:- 66.44+0.22(8-1)66.44 as an example

Step 1 is evaluate the brackets (8-1) = 7
Step 2 is evaluate the multiplications 0.22 x 7 x 66.44 = 102.3176
Step 3 evaluate the addition 66.44 + 102.3176 = 168.7576

And to see it using something simpler:-

1 + 2 x 3 should equal 7 but if you get it wrong it might be 9, which would equate to (1 + 2) x 3

Hope that helps for anyone that doesn't have kids handy to explain it to them :)

Indices and orders for those that aren't familiar are things like 2 squared and square root.

Edit:- You may also see "." being used to indicate multiplication but this is less common as it has the potential to be confused with the dot product in relation to vector and matrix math.
 
Thanks for taking the time to explain that SC :thumbsup:
Really is a struggle for someone like me who has to relearn everything every few years when it comes to maths. I'm hoping to refresh myself on basic transposition of formulae soon as that never sunk in to a permanent state either.
 
In my copy it is definitely 66.44 + 0.22 (8 - 1) 66.44.

Which is as I've described. 66.44 + (0.22 x (8 - 1) x 66.44)
Perhaps I’ve actually got a dud copy?
Does yours have the mistakes I described earlier such as using old reference method numbers and on the same page using 1.44 ohms max zs for type b 32 amp mcb then using the correct 1.37 ohms?
Think it’s when it’s describing max lengths of a ring circuit I’d have to dig it out to check the page number for where it’s at?
 
Perhaps I’ve actually got a dud copy?
Does yours have the mistakes I described earlier such as using old reference method numbers and on the same page using 1.44 ohms max zs for type b 32 amp mcb then using the correct 1.37 ohms?
Think it’s when it’s describing max lengths of a ring circuit I’d have to dig it out to check the page number for where it’s at?

I have a counterfeit copy of GN3, got it from Amazon. It was explained to me that small errors like that and spelling mistakes occur through the counterfeiters using scanners to "read" the pages of the original and reprint it. These scanners, or the software that interprets the scan, are prone to mistakes.
 
Andy is correct and it is a misprint as I have the same book.
In fact there’s several mistakes in it such as giving the max zs of a type b 32 amp mcb as 1.44 ohms then directly underneath or above this example it gives the correct figure of 1.37 ohms.
Also uses old reference methods such as reference method 1 and reference method 3 etc.
Still a decent book tho.

Yes, it has those values on page 25.
 
I have a counterfeit copy of GN3, got it from Amazon. It was explained to me that small errors like that and spelling mistakes occur through the counterfeiters using scanners to "read" the pages of the original and reprint it. These scanners, or the software that interprets the scan, are prone to mistakes.
MY design guide was bought through amazon cant remember if it has the iet hologram on or if that’s just bs 7671 and on site guide publications.
 

Reply to Complex Installations demand calc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock