Discuss Conductor Operating Temperature H07RN-F in the Industrial Electricians' Talk area at ElectriciansForums.net

CPL

-
Reaction score
0
Hi All,
I'm trying to calculate CCC & VD for H07RN-F Single core cable. Used for event powerlock runs.
TPN AC - Ref Method C - Flat & Touching
Table 4E1A/B covers Single Core 90*C thermosetting insulated cables, which I have used correction factors to convert these values to flexible cable but looking at the spec of our cable, its rated at 60*C Conductor Operating Temperature.
Is there another correction factor that I can apply to Tables 4E1A/B to reduce the characteristics to 60*C rated cable, or have I got the wrong end of the stick!
Many thanks
 
The 4F... tables are for flexible conductors.
If you still want to use rigid conductor cables tables to consider the installation method then at least 70°C tables would be better than 90°C.
 
Hi All,
I'm trying to calculate CCC & VD for H07RN-F Single core cable. Used for event powerlock runs.
TPN AC - Ref Method C - Flat & Touching
Table 4E1A/B covers Single Core 90*C thermosetting insulated cables, which I have used correction factors to convert these values to flexible cable but looking at the spec of our cable, its rated at 60*C Conductor Operating Temperature.
Is there another correction factor that I can apply to Tables 4E1A/B to reduce the characteristics to 60*C rated cable, or have I got the wrong end of the stick!
Many thanks

Table 4F1A is for CCC of 60° flexible cables.
Table 4F1B is for the VD
 
To expand on my above response the terminals in powerlock connectors aren't rated for 90 degree operation as far as I know so the 60 degree rating for the cable needs to be used.
Also I was told many years ago that the 60degree rating is used for this application because the cables are exposed to touch, I'm not fully convinced by this though as conductor temperature doesn't equal outer surface temperature.
 

Reply to Conductor Operating Temperature H07RN-F in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

According to note 8 of table 4c1 of bs 7671, cables of differing operating temperatures when grouped together, the current rating is to be based...
Replies
4
Views
469
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
At work in our main kitchen, the 6kW (26A sp) water packed up. The restaurant staff were in turmoil, as they had no hot water to make the tea...
Replies
21
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock