Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Conduit as earth???? in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. mickytuff
    Offline

    mickytuff Regular EF Member

    Hi all done some testing work at a hospital and the orignal wiring was done in metal conduit, now the zs figures tested all good, my question is can u calculate the r1 and r2 figure when their isnt an earth cable as such???
     
  2. Edd
    Offline

    Edd Guest

    Good question,, as for r1 thats your line conductor, and r2 being your earth in this case the conduit. in this set up I use a wander lead and zero my meter with this long lead. then go around pokeing it onto every acessory's earth the highest reading I take as my r2 reading for the test cert
     
    • Like Like x 1
  3. Guest123
    Offline

    Guest123 Guest

    You cant calculate R1+R2 from Zs anyway, even if a seperate cable was being used as CPC due to all parallel paths included when live testing Zs.
     
    • Like Like x 1
  4. nickblake
    Offline

    nickblake Electrician's Arms

    biggest probelm is if the conduit is broken you should really do a Zs at every point to confirm polarity and earth continuity ,what you should do is an r2 test instead of the r1r2 but note it on the test certs as conduit used as earth
     
  5. Edd
    Offline

    Edd Guest

    LOL,, should have read the post better!! didnt see the calculate bit thought he was asking how to take the reading.. my bad.. :)
     
  6. mickytuff
    Offline

    mickytuff Regular EF Member

    So on the cert in the earth continuity box what would you put l/l n/n and then????? I agree doing the r2 method to confirm the earth, which is also confirmed by doing the zs test but do i leave the box blank or put n/a due to the nature of the wiring system used????, oh and thanku all for your ideas, all gratefully recieved, shud of said that 1st realy
     
  7. Edd
    Offline

    Edd Guest

    I put con or mech in the CPC box for ring mains, and would put a - in the r1-r2 box and put my r2 reading in the r2 box :)
     
  8. Guest123
    Offline

    Guest123 Guest

    I'm confused even further now.

    Are you referring to the section for the cable sizes i.e 2.5/1.5 for a normal RFC??? Where conduit is used as the CPC, under the CPC size i enter 'K'.

    For the measurements, L-L (r1), & N-N (rN) are as normal, for E-E (r2), again I put 'K' in the box.
     
    • Like Like x 1
  9. Edd
    Offline

    Edd Guest

    thats the way I read it lenny,, but i have to say can you tell me about the 'K' ive always put mech or con in them places..
     
  10. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    Konduit???
     
    • Like Like x 2
  11. mickytuff
    Offline

    mickytuff Regular EF Member

    When testing i use the amtech software and you can select the earth as conduit, you enter in the size of the conduit and it gives you a equivelant figure as a c.s.a of 80mm for 20mm conduit, meaning the conduit is acting like the size of a 80mm cable i presume, strange i know, but this figure cant be accurate, as the condiut could be 1m long or 30m in length, so this isnt realy accurate, the column i was reffering to was the ring final contuity part, what i've just said is the column your referring to, i.e the cable size part.
     
  12. mickytuff
    Offline

    mickytuff Regular EF Member

    I understand what your saying lenny, you put k in the e-e box and enter your r2 reading in the r2 box, as you cant calculate the r1/r2 conventially? Correct?
     
  13. mickytuff
    Offline

    mickytuff Regular EF Member

    So you ready for my next question???
     
  14. nickblake
    Offline

    nickblake Electrician's Arms

    braced and waiting lol
     
  15. mickytuff
    Offline

    mickytuff Regular EF Member

    Ok nickblake here we go...............while testing with a megger multi, if you chose to test on notrip on your loop test, why do U have to connect all three leads, if you connect just line and earth it wont produce a reading and just say trp on the display, yet when you deselect no trip it tests fine with just two leads connected, so there you go, any body else had same problem???????????
     
    Last edited: Feb 1, 2012
Loading...
Similar Threads - Conduit earth Forum Date
Steel Conduit Bending Writen guide. Electrical Forum Monday at 12:22 AM
Round conduit box lids. Electrical Forum Mar 10, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job