Discuss Conduit cable calcs....help please ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

sythai

-
Arms
Reaction score
356
Just calculating my In... conduit with singles run.

For the grouping factor - Cg it states number of circuits

If I have 2 circuits, but this consists of 18 x singles (e.g 1 x ring = 6 and 4 x radials)

Would this still be a factor = 0.75 ?

Thank you

Sy
 
You have 2 circuits?
The rfc I can understand but you now have 4 radials?
1/ Are these 4 radials connected to the same breaker?
2/ When calculating the grouping factor, why do you include the cpc ?
3/ Have you looked at the space factor rather than the grouping factor?
 
You have 2 circuits?
The rfc I can understand but you now have 4 radials?
1/ Are these 4 radials connected to the same breaker?
2/ When calculating the grouping factor, why do you include the cpc ?
3/ Have you looked at the space factor rather than the grouping factor?

1/ The 4 radials start as 32amp kitchen appliance ring and then go into 4 x FCU and its the load sides from here that are going down the conduit, so all on the same breaker.
2/ Never had to work out grouping factor before (about 15 years ago at college) just didn't realise that all, thats why I'm on here figuring it out:)
3/ Calculated space factor and it's just under - have only got a 2m run with one bend - 25mm tube
 

Reply to Conduit cable calcs....help please ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Hi, folks.' I have a carrier 38MGRQ48E '5 zone' mini split system with 4 'heads'/evaporators installed, and one 'channel' still open. Had it...
Replies
0
Views
639
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock