As i don't really do much proper conduit work, i have what may be an obvious question to some. Within a PVC installation, if you had 2 phases feeding a light switch for 2 lots of lighting, would there be a cpc pulled in with both the feeds, or is it done with just the cpc from one circuit at the switch?
 
i would put 2 cpc's in. 1 for each circuit. otherwise, you are effectively splitting a cpc between 2 circuits.
 
run the cpc's from the dis. board to the switch position, then separate to each run of fittings.
 
i would put 2 cpc's in. 1 for each circuit. otherwise, you are effectively splitting a cpc between 2 circuits.

Just playing devils advocate here Tel, but I can't see anything wrong with splitting a single CPC between two circuits so long as the csa is an appropriate measurement.
 
Just playing devils advocate here Tel, but I can't see anything wrong with splitting a single CPC between two circuits so long as the csa is an appropriate measurement.
not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.
 
I'd take one CPC to the switch to earth the switch; if you 'had' to take a CPC for every live you might have each switch on a different cct so you could end up with about 20 cpcs in the switch, which would be silly.

Because it's being done in singles the CPCs for the lights can go straight from the CU to the lights, with the neutrals.
 
would that not contravene "all final circuits to be segragated" though Mr Skelton?

Check out reg 543.1.2. Where a protective conductor is common to two or more circuits...

not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.

Me too. I agree, I would pull two CPC's through too. I'm just sayin', that's all ;)
 

Reply to Conduit installs in the Australia area at ElectriciansForums.net

Similar Threads

BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Replies
5
Views
876
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
When there exists a single-phase transfer switch within a 3-phase distribution system, is it necessary for both feeds to the transfer switch to be...
Replies
8
Views
732
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
724
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
894

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock