Hi Guys just a quick question but what the hell do I put in confirmation of earthing conductor size when the earth is the swa
Refer to the Table Buzz has provided
 
I've already checked the table but it's not the csa I'm after which option on ecr do I put pass/na/nv etc
refer to the chart it will give the size equiv to CU
 
I'm filling out an EICR on a landlord supply there is a small consumer unit fed by 25mm 2 cire swa from an isolator which is fed from 25mm tails from a meter with a 16mm earth my question is how can I confirm the conductor size to the consumer unit when it is swa
 
If your earthing system is TN-C-S then the armour is inadequate to support main protective bonding.
 
Use table 54.7 of bs7671.
Or the Adiabatic equation for CSA of armouring for use as the cpc
 

Reply to confirmation of earthing conductor size in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock