Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss confused with procedure need help in the New Member Introductions area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    installed a secondary 2 way consumer unit to run a boiler and immersion heater i know i have to issue an eic but what do i actually test? r1 + r2 of the radial to the secondary consumer unit and both radials from the secondary consumer? please can someone give me a rundown of what id need to test?
     
  2. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Yes..... And obviously part P
     
    • Agree Agree x 1
  3. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    what do you mean part p?
     
  4. Rosco
    Offline

    Rosco Electrician's Arms

    Location:
    Maidstone
    This is a wind up right?
     
    • Like Like x 1
  5. soms
    Offline

    soms Trainee Access

    Location:
    Somerset
    You will need to perform all the tests required to complete the fields on the EIC. Methods for performing these tests are described on your On-Site Guide.
    If you have installed new circuits in a domestic property this is notifiable work under the Part P of the Building Regulations and you are required to notify the Local Authority Building Control.
    I assume you are not able to self-certify the work so can expect to pay them for the privilege of inspecting it for you.
     
  6. Andy5678
    Offline

    Andy5678 Electrician's Arms

    Location:
    Scotland
    Have 2 schedules of test results one for the first CU showing your new circuit to the 2 way CU and the other schedule showing the new circuits on the CU that you installed. 1 inspection sheet and all the other details needed. All tests required apart from ring continuity if you have no ring finals
     
  7. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    yes i know you have to contact building control you ever tried talking to newham building control? they dont even know what they are doing. ive got 2391 and 2392 but get told all different things some people saying you have to re test the whole board even the old circuits which i didnt think was right i just thought it was the new circuits your installing you had to test
     
  8. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    t6h

    thankyou andy
     
  9. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Your description of works on the EIC is what you need to do ..



    So something like ..... Install new circuit number ?? And install 2nd fuseboard and new circuits for .....

    You have to ensure earthing and bonding are up to spec, plus your circuits must comply with the latest regs.

    On your schedule of results for the existing board, I would use state "used" for existing circuits, and spare for any unused.
     
  10. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    cheers murdoch all earthing is within the regs and my instal is withing the regs so its just a confusion on what to test to make sure my eic is correctly filled out
     
  11. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    With your qualifications how come you don't know about the certificates.

    You need to deal with the part.p
     
    • Agree Agree x 2
  12. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    The Certsure on-line certification, uses the phrase 'NOT WOKED ON' for those circuits, not worked on! Succinct and to the point.
     
  13. danny harding
    Offline

    danny harding EF Member

    Location:
    london
    b
    because im newly passed and cant remember everything down to a t on the testing side so im just double checking
     
  14. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    The notification of your new circuits is an issue that needs consideration. Have you done this job for financial gain?
     
  15. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    It's R1+R2, r1,r2and rn are end to end resistances.
     
    • Agree Agree x 1
Loading...
Similar Threads - confused procedure need Forum Date
Help! I’m confused to what I’m entitled to New Member Introductions Mar 5, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job