Testing existing installation, notice one circuit that supplies 10 * 30 watt LED lights has a 16 amp mcb protecting it. Change the mcb to 6 amp and it instantly trips, thought maybe I'm missing more light fitting on circuit. Used my clip on ammeter and it reads 1.7 amps, all dead tests and live tests are fine. Then thought maybe a high inrush of current, changed mcb to type c and it still trips but change it back to the 16 amp mcb and it works fine. Am I missing some thing here.
 
Your cable size will determine the rating of the protective device,not the load connected to it. The purpose of the protective device is to protect the cable. If your cable is suitable for a 16a MCB, then leave it in.

Cheers………….Howard
 
The cable is 1.5 mm and in some places 1mm. Zs is 1.27 ohms. Calculated amps came to 1.3 amps and ammeter isn't that far away from that measurement. If the cable wasn't 1 mm in places I would have just left it. Thanks for your input on this guys.
 
... has a 16 amp mcb protecting it. Change the mcb to 6 amp.
Why would you change the MCB for a lower value?? As per post#5, put the 16A back unless there's a good reason not to.
 
If it ain't bust, don't fix it!!!!!!!!!!!!!!!
 
The cable is 1.5 mm and in some places 1mm. Zs is 1.27 ohms. Calculated amps came to 1.3 amps and ammeter isn't that far away from that measurement. If the cable wasn't 1 mm in places I would have just left it. Thanks for your input on this guys.
so...whats the install method on the 1.0/1.0?

its good for 16A method C
 

Reply to confused in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock