Discuss connecting 415v 3 phase motor in the Canada area at ElectriciansForums.net

L

lkpflk

i have replaced a 415v 3 phase motor at work. The old one had 3 terminals in a line, each with one internal wire connected, and one terminal on other side with 3 internal wires connected. The new one has 6 terminals, each with one internal wire connected. It came with 3 bridging links which i have used. However, when i run motor, it trips on overload after about 20 seconds, and blows a fuse. It also feels warm. Obviously, it is not connected correctly. Would appreciate any help. Thanx.
 
is the new motor same size/spec. as old one,check plate on motor ,when you connect motor are you connecting it in star or delta (check where you put the links)what size is the motor kw
yours benji
 
it is a 7.5kw motor, and the same spec as old one. As for star or delta, i don`t know. Just want it to work. Thanx.

sorry, that should read 0.75kw.
 
Last edited by a moderator:
it sounds like the old motor was connected in "star" configuration

to achieve this the links need to go across the secondary terminals rather than between the two sets
 
Read the rating plate and see what it says . Connect links accordingly.

Would draw a picture but dont know how, not much good with computers, but in star, the 3 phases need connecting to U1 V1 W1, and the links want to be accross U2 V2 W2.

In delta it should be the three phases conected to U1 V1 W1 and then linked as follows, U1 toW2, (one link) V1 to U2 (second link) and W1 to V2 (last link)

This is providing it is a standard motor with nothing oddball about it, would be worth checking to see if you have all three phases at the motor, and putting the clamp meter on under load conditions and setting overload accordingly. Have you found out what knackered the old one, because if there is say a phase missing, or a dodgy contactor, then the new motor probably wont last long either.

Let us know how you get on.
 

Reply to connecting 415v 3 phase motor in the Canada area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
645
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock