Hi Nick, A few thoughts in addition to NDGs good points.
Meter tails item 7.7 - reg 521.5.1 says (in last part) 'does not preclude the use of an additional protective conductor ... to enter enclosure individually'. To me, the expected method is for line, neutral and protective conductor to enter together. IMHO what you have is functionally safe due to current levels, but may well be questioned. So have a close read of 521.5.1 and be ready to discuss.
Also, I think you might be questioned about IR > 2meg results. It is expected that this be the actual result you measured. A result near 2meg would be widely viewed as needing further investigation. Just saying.
A couple of others to confirm :
Max demand is 35A ?
Metal partitions are ticked in 8.14 ?
Adequacy of working space is blank in 9.4 ?
Hope that helps :)
 
IR is normally recorded as the reading your test kit shows not that its above the required resistance.
 
I hope you are going to submit nice neat paperwork and that is your trial run. I believe if your paperwork is untidy this gives an immediate poor impression.
 
As a slight deviation has anyone re-generated these forms to be easier to use?
The actual layout isn't great and many entry locations are just too small to enter details in a legible way.
 
I hope you are going to submit nice neat paperwork and that is your trial run. I believe if your paperwork is untidy this gives an immediate poor impression.
Think that's his 'working copy', well I hope so. I use to do that, until I lost a page of test results. Now use a desk diary, harder to lose :rolleyes:
 
Thanks for all the input. I recorded ir as >2 as that's what the electrician I used to work for did. I note your points and will re-record the actual measurements tomorrow (they were all greatly in excess of 2 - none were under 600).

I'll call elecsa first thing tomorrow morning and ask their view. If they want it coming through the back then I'll need to scramble in order to get it done tomorrow as assessment is Tuesday!

Those results are indeed just a working copy. I'll use an electronic system after assessment but that system isn't in place yet.

Nightmare scenario!
 
To pick up on maximum demand question.

I've put 35A. I came up wih that figure by adding all the breakers together and taking 40% of their total as maximum demand.

I see maximum demand done in so many different ways and I see different opinions on it.

Some say add all breakers and put that result regardless of whether it's greater than main fuse (an approach I'm not keen on?)

Some will use osg and put that figure.

Some use the 40% rule.

I have 32a ring (no diversity can be applied)

32a cooker circuit (I think I worked it out at 27a using diversity)

16a heating (no diversity allowed if immersion - unsure if there is one, then unsure how to calc if there isn't one)

6a lights - 8 lights in house, allow 100w per light so 800w, 3.5a.

Adding all that is greater than 60a.

What would you guys put?
 
Thanks for all the input. I recorded ir as >2 as that's what the electrician I used to work for did. I note your points and will re-record the actual measurements tomorrow (they were all greatly in excess of 2 - none were under 600).

I'll call elecsa first thing tomorrow morning and ask their view. If they want it coming through the back then I'll need to scramble in order to get it done tomorrow as assessment is Tuesday!

Those results are indeed just a working copy. I'll use an electronic system after assessment but that system isn't in place yet.

Nightmare scenario!

IMHO thats a terrible way to do it and train you!

I can only assume that he did a global IR to achieve such numbers but in reality its a very unhelpful way of doing it when doing a CU change and introducing RCD's.

I always test IR before using a global measure (as a check) but then as the new CU takes "shape" I connect ALL the CPC's to the CU and test all the circuits individually L-N, L-E and N-E - that way you will see the "real" situation in the install.

It would seem that many people do the global IR as L&N to earth, which is simply lazy - the only way to check the installation IR properly you need to isolate as many of the appliances as possible......

As an example I did a global IR recently and got really terrible L&N to E readings - so went round unplugging as much as possible and then found it was 1 circuit in particular - further searching revealed a RCD FCU in the back of a cupboard - so this was swapped for a std unit and the readings improved dramatically
 
I also checked each individeally murdoch (as did the electrician I worked for) I just put the >2 as that's what I believed should be entered.

I take notice of what's been said here and will remeasure and record them tomorrow.

Depending on what elecsa say I may need to remove the board to bring the main earth through the rear so taking ir again wont be much more effort.

I do hope they are happy for main earth to come through separately as to get all that work done the day before assessment is cutting way too close!
 
The reason we state the measurement we get is that you may well get a result that's well above 2 mohm but lower than your kits max reading. That value is important as later measurements may show a degradation in IR.
So we record the actual meter result and that's implicit its greater than the minimum reg requires.
 
Midwest, I have read that thread and I note what you said in one post

"Thought I would invest in the latest copy of Guidance note 1, Selection & Erection. Curious, I looked up 'Ferromagnetic enclosures, cable entering; (521.5.1) All the conductors of a circuit should generally follow the same route. Live cables of the same circuit may cause overheating if they enter a ferromagnetic enclosure through different openings (page 97, 7.4)"

I don't own gn1, I'm slowly buying and reading them all however gn1 is not one I've bought yet.

Reading that further confuses me. all conductors "should" not "must" therefore surely not required? I understand that l and n could cause issues but I don't see a problem with main earth coming through a separate hole.

I do hope elecsa can give me a definitive answer tomorrow at 8am. I'm worried about finishing on time of I have to reroute it all now.

Stress levels through the roof right now.
 
Unless under fault conditions no current flows in the CPC so eddy currents related to that are immaterial. So as long as the L & N are together then fine.
 
Wouldn't lose sleep over earthing conductor through a separate entry, Pat is quite correct. Put your IR as >500 as >2 indicates a problem.
 
Don't stress too much Nick! The assessors are usually fine n easygoing. I would bring the point up with him about the main earth and have some other tech questions at the ready to; they like that kind of stuff!

Get a couple of packets of taste the difference cookies and you will be fine....
 
Pat, I agree and I saw no reason not to run the earth through a separate hole until I read on this forum about 521.5.1.

Paragraph one is met as they are all in same enclosure.

It's paragraph 2 that causes issues,

"Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferromagnetic material"

Paragraph 3 is irrelevant I think in my case as the tails aren't SWA.
 
In your experiences, would something like this cause a fail or deferral? I really can't afford for another assessment both financially and more importantly time wise.
 
I also checked each individually murdoch (as did the electrician I worked for) I just put the >2 as that's what I believed should be entered.

I take notice of what's been said here and will remeasure and record them tomorrow.

Depending on what elecsa say I may need to remove the board to bring the main earth through the rear so taking ir again wont be much more effort.

I do hope they are happy for main earth to come through separately as to get all that work done the day before assessment is cutting way too close!

Recording the individual circuit readings is the best way to go ..... because if you called back later for, say tripping, you can compare readings to see if any have changed.....

There is NO requirement to bring the main earth through the same aperture as the tails..... so don't waste your time making the call. There are special glands that allow you to bring the tails and earth together but that's a "nice to have" .
 
Yes but that relates to conductors conducting currents and the issues with eddy currents. The CPC isn't normally conducting so irrelevant.
I'd raise it with the assessor and say you've considered the regs and the reasons (you can even add you've taken advice) and you are happy with your solution.

I'm not in a scheme yet. hoping for my niceic assessment in the next month or so but in no rush.
 

Reply to Consumer Unit Change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
722
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
632
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock