RCD– is the Generic Term applied . :20:

RCCB:- Residual Current Breaker .
RCBO:- Residual Current Breaker withOver-current protection .

An RCCB differs from an RCBO in thatthe RCBO will additionally respond to over-current conditions whereas the RCCBwill NOT respond to such conditions .

Apprentices : RCDs

The magnitude of thecurrent flowing to the Load will equal the magnitude ofthe current returning from the Load back to the supply .
Any difference in the current flowing to the Load &returning from the Load is known as a ( Residual Current ) – Dual / Two / Line & Neutral :svengo:

 
Apprentices : RCDs

Values of Rated ResidualCurrent ( I∆n )

RCDs– can be provided with any value of Residual Current Operating Current ( I∆n ) .
10mA: 30mA : 100mA : 300mA : 500mA : ↔ 704.4.1.1.3.2.1. :20:

30mA : isthe maximum value permissible for additional protection & 300mAis the maximum value permissible for fire protection.
Non-standard values may be Used . BUT the Additional Protection & Fire must NOT beexceeded . :svengo:

 
Apprentices : RCDs :hurray:

OperatingTimes .

RCDsfall in to two categories in terms of the time taken to respond to & clearResidual Currents’ .

Regulation table - 3A . Appendix 3 – Informative . p/243

General Type :- These RCDs have no specified minimum responsetime but have specified maximum response times as follows .
I∆n ≤ 300mS ↔ Note:- BS-EN
I∆n ≤ 40mS

S Type :- These RCDs have no specifiedminimum response times but have specified maximum response times .
I∆n ≤ 130 – 500mS
5 . I∆n ≤ 50 – 150mS

Delayedresponse ( S – Type ) RCDs are commonly fitted Upstream of general type RCDsbut general type RCDs should never be fitted Upstream of Delayed Types .
The “ Term “ Upstream. refers to proximity to the origin of the Installation & “ Downstream “ refersto proximity to the Load .




 
Apprentices : RCDs :bulb2:

Maycomprise One or Two poles for use on Single-phase supplies . ( Two currentpaths ) . Three-poles for use on Three-phase supplies . ( Three-current paths ) or
Four-polesfor use on Three-phase & Neutral supplies( Four-current paths )

 
Inspection& Testing of an installation should be completed by . A competent person

ByDefinition . RCDs :17:

A.C.current comprises of Positive & Negative half cycles with respect to a Zero reference point . & an A.C. fault current canstart to flow to Earth at any point during either half cycle . An A.C. type RCDwill only trip in response to either the Positive &Negative half cycles of the A.C. Earth faultcurrent .
Whereasas ( A ) type RCDwill respond to both half cycles . As the A.C. type RCD is Blind to either the Positive & Negative halfcycles of the A.C. fault current .
Thefault current could flow for up to 10mS before the RCD will see the faultcurrent .

This10mS will be added to the response time of the device .
RCDtesters are usually provided with a button to enable the user to start the flowof the test current at ( 0 degrees / 180degrees ) starting on a Positive goingor a Negative going half cycle respectively .

Bystarting the testing of the RCD at both settings of the test current conductionangle . The user will be able to determine the maximum trip time of the RCD .
Thiscan be done at different test current levels .

 
Calculationof Earth Fault Loop Impedance :speechless:

The most commonly used measure . Automatic Disconnectionof supply either the Overcurrent protective devices - Which also provideprotection against “ Overload &Short circuit Currents for the circuit Concerned .

ResidualCurrent Devices . RCDs or combined devices RCBOs . Whichever type of device ischosen .

TheEarth Loop Impedance that has to be considered is that which comprises the Impedance of the Source .
TheLine conductor up to the Fault plus the Protective Conductor from the fault to the Source .

Whys& How’s .

Note:- That when an RCD or RCBO is used to provide Automatic Disconnection of thesupply in a ( TN- system ) the calculation of ( Zs ) is normally “ Unnecessary “ provided that “ Continuity“ of the EarthLoop has been Established . ◄◄

Anotherreason for calculating the Earth Loop Impedance is to check that the “ Circuit Protective conductors are adequatelyprotected thermally . & That they comply with the “ Adiabatic Equation givenin Regulation . 543.1.3. – Subject ofChapter 4 .


 
BS-7671:2008– Bottom of . Table 41.3 – NOTE.

ContainsNO requirements in relation to the Conductor Temperatureat which the Earth Loop Impedance iscalculated .
Note :- The notes to the tables of Maximum Earth FaultLoop Impedance . – Table 41.2. – to 41.4. . States . that the Tabulated Valuesshould NOT be exceeded when the conductors’ are at their Normal Operating Temperature.

ifthe conductors’ are at a different temperature when tested . The reading should be Adjusted Accordingly – Appendix 14.

 
Current – Carrying Capacity . ofa Conductor . :speechless:

TheMaximum Current which can be carried by aconductor under Specified Conditions without itssteady state temperature exceeding a specified value.
 
Apprentices.

Namethree types of “ Diagram “used in the Electrical Industry . & explain – ThereUse . :icon_bs:

Anythree from Wiring diagram . Circuit diagram . Block diagram . Layout drawing .Installation drawing . Schematic drawing . Site plan .

A wiringdiagram provides a pictorial representation of an Electrical Circuit . showing arepresentation of the components .
A blockdiagram typically shows the flow of aprocess . each function being represented by a block .
A schematicdiagram uses symbols to show the arrangement of a system clearly .
Whereasa layout diagram shows the physical arrangement of the wires & components .


 
:45:2392-10: ▼
Q) The main switch in a “ Single Phase “ domestic Installation interrupt’s how many “ Live Conductors

-&-s: BS-7671 – Regulation 537.1.4. The main switch should interrupt both LiveConductors on a Single/Phase Supply .

A MainSwitch intended for operation by “ Ordinary Person“ of a Household or similar Installation . shall Interruptboth Live Conductors of a Single-phase supply .

Q) How many poles would the main switch on aThree-phase & Neutral – TN-S supply have .

Threepoles - BS-7671 – Regulation 537.1.2. The Neutral neednot be Switched . ( TN-S or TN-C-S )

2392-10: ▼

Q) State: Two precautions that must be takenbefore carrying out Insulation Résistance Testing .

i) Remove sensitive equipment – Dimmers .Programmers . P.I.R.
ii) Remove equipment that “ GIVES “ falsereadings – Lamps . Neon’s . Motors .
iii)Check it is Safe to continue with the Test . When applying – 250 / 500V .

-&-s: Make sureNo-one else is in contact with any part of the Circuit .
 
2392-10: ▼

Inrelation to Electrical Installations . :waving:

Whatis meant by Maximum Demand :- This is an Assessment of the current demand of an Installation.
Whatis meant by Discrimination :- The co-ordination ofprotective device(s) so that the device nearest to the load . being of a lowerrating . operates before the device futher up the line . Thereby minimisingloss of supply when a fault occurs .
Whatis meant by Diversity :- An allowance given when calculating maximum demand . due tothe fact that not all of the appliances . will be Used at the Same Time .
 
2392-10:

ApprovedVoltage Tester . To - GN-38 . :waving:
State:- Three of the requirements for Test Leads .
i) Retractable tips . or not more than ( 4mm) prefer 2mm . Fingers guards . Robustleads . coloured or identified . long enough for the purpose . Fused probes .

State:- the method of Ensuring it is working Effectively .
ii) By the use of an Approved Proving Unit .Testing the voltage tester . Before & After testing the equipment . or Circuit .
 
Definitions’/ p/23 . EarthingConductor

A protectiveconductor connecting the main Earthing Terminal of an Installation to an EarthElectrode or to other means of Earthing .

Connectsthe main Earthing Terminal to the source of Earth . either an Electrode ( TT ) or means ( TN-S or TN-C-S ) :95:
 
Insight to the working of 17[SUP]TH[/SUP] Edition . “ Examples “

BS-7671:2008. Section 708 – Caravan & Camping Parks .

Thisis accommodated by the provision of suitably placed socket outlets . supplied via distribution circuits .

External Influences .
Equipmentshould have at least the following protection codes .
Impactrésistance . 708.512.2.
IPX4– for the presence of Splashes – ( AD4 ) in accordance with BS-EN 60529.
IP3X– for presence of small objects - ( AE2 ) in accordance with BS-EN 60529.
IK08- for presence of high severity mechanical stress ( AG3) in accordance with BS-EN 62262 .
(The ( IK ) codes are for Impact & ( 0.8 ) is an Impact of ( 5-Joules ) ImpactRésistance .
( Environment – p/324 . AG3 – High Severity . Reinforced Protection . IK08 )

British Standards to whichReference is made in the Regulations . Appendix1 – “ Normative “ p/228 – ( Requirement )

BS-EN 62262:1992 . – 2004 . Specification for degrees’ ofprotection provided by enclosures ( IP Code )
527.2.6.– (i) the system satisfies the test of BS-EN 62262 for ( IP33 )
527.2.6.– (ii) any termination of the system in one of the compartments , separated bythe building construction being penetrated . satisfies the test of BS-EN 62262for ( IP33 )
702.512.2.: External Influences . Electrical equipment shall have at least the following degree of protection according to BS-EN 62262. ( IP ???? )
708.512.2.- (i) & (ii)
708.553.1.8.each socket-outlet & its enclosure forming part of a caravan pitch electricalsupply equipment shall comply with ( BS-EN 60309-2 ) & meet the degree of protection of at least( IP44 ) accordance with BS-EN 60529 .
A721.55.6.- p/218. Terminal blocks .
A721.55.10.- p/218. External lights .

Note : Section 721 : tells us . p/209 – Wording . Yeah :96:
Inorder not to ►► MIX ◄◄ Regulationson different Subjects such as those for Electrical Installation ofcaravan parks with those for Electrical InstallationINSIDE caravans .
Section– 708 . concerns Electrical Installations ( IN ) caravanparks . camping parks & similar locations & . Outside.
Section– 721 . concerns Electrical Installations ( IN ) caravans& motor caravans . Inside

WiringSystems .
Thedistribution circuits are erected either Underground or Overhead .
708.521.1.1.- i) Underground cable ( Preferred )should be suitably protected against Mechanical damage . tent pegs . steelspikes . & at a depth of NO less than ( 0.6m )
708.521.1.2.- ii) Overhead . if overhead . Then ( 6m) above ground where there is Vehicle movement ( 3.5m ) elsewhere .

Switchgear& Socket outlets .
708.530.3.- Supply equipment should be adjacent to . or within ( 20m ) of the pitch .
708.553.1.8.– Socket-outlets should be :- BS-EN 60309-2– ( IP44 )
708.553.1.9.- at between ( 0.5m to 1.5m ) aboveground .
708.553.1.10.- rated not less than ( 16A )
708.553.1.13.– each socket-outlet shall be protected individual by an ( 30mA ) RCD protection. ( The device shall disconnect all LIVE CONDUCTORS including the NEUTRAL.
708.553.1.14.– if the supply is ( TN-C-S ) the protective conductor of each socket-outletneeds to be connected to an ( Earth Rod ) Regulation – 411.5. TT System .
 
AdditionalProtection . :hurray:

703.411.3.3.Sauna heater .
Allcircuits in the location should have “ Additional Protection “ against shock by30mA RCD .
Except Sauna heater circuits unless Recommended by the Manufacturer . :svengo:


 
External :- Earth Fault Impedance . ( Ze )

The Importance of this Test . To establish that a good Earthexists at the installation in order for the Remainingtests to go ahead . :svengo:
 
Additions & Alterations to anInstallation . :waving:

General :

Many existing electrical installations require one or moreAdditions or Alterations during their lifetime . An Addition or Alteration maybe minor ( such as the Addition of a point to a final circuit . or therepositioning of a point ) or major ( such as the Addition of a new finalcircuits . distribution circuits . distribution boards & an upgrade to thesupply .

Where an Addition or Alteration ( which temporary or permanent) is to be made to an installation . the relevant requirements of BS-7671 .have to be met such that both the Addition or Alteration is Safe . & thesafety of the Existing Installation is not Impaired.

In order to be meet the requirements of BS-7671 . Followingmust be undertaken .

Assessment ofthe existing installation to establish that the parts upon which the Additionor Alteration will rely for safety are both present & suitable for thealtered circumstances . & will continue to be so . & that the supply issuitable .
• Upgrading of parts of the existing installation . where foundnecessary to safely accommodate the Addition or Alteration . as a result of theabove Assessment .
The electricity distributor will need to upgrade thesupply . if Necessary .
• Design & construction of the Addition or Alteration inaccordance with the requirements of BS-7671 .
(T) • Inspection &Testing of any upgrading of the existing installation . & of the Addition or Alteration . as requiredby chapter 63 of BS-7671:2008
Certification of any upgrading of the existing installation . & of the Addition or Alteration . as requiredby chapter 63 of BS-7671:2008

Assessment of an Existing Installation .
Regulation ( 131.8.) requires an Assessmentto be made of the relevant parts of an existing installation which is tobe Added to or Altered of the Supply .

Regulation ( 131.8.) No Addition orAlteration . temporaryor permanent shall be made to an existing installation . unless it has been ascertained thatthe rating & the condition of any existing equipment . including that ofthe distributor . will be Adequate for the Altered circumstances . furthermore . The Earthing & Bonding arrangements . if necessary for theprotective measured applied for the safety of the Addition or Alteration . shall beAdequate .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Replies
36
Views
15K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock