Im currently studying electrical and im up to dead tests.

ive reached continuity of ring final circuit on my scenario cd , in therory i understand the procedure and what to do but im a little un sure on finding the mid point on the sockets .

please can sombody go threw it step by step in detail

thanks
 
Do R1+R2, the socket with the highest reading should be the mid point if it's part of the ring, spurs will be higher so don't take that as the mid point.
Hope this helps.
Paul.
 
why the interest in finding midpoint? the rfc test is designed to prove integrity of the al of the rfc conductors and in doing so the values of R1 + R2 are found along with dead polarity when tested at the front of socket outlets on Step 3
Step 1 open loops end to end

Step 2 interconnection of opposite leg lives, sum of open loop r1 + rn over 4 at s/o, readings to be substantially the same any spurs will be higher


Step 3 interconnection of opposite leg line and cpc, sum of open loop r1 + r2 over4 at s/o readings to be substantially the same any spurs will be higher, highest reading is recorded as R1+R2

and as it you go round not withstanding any loose connections or spurs you will find your midpoint
 
If you really wanted to find the mid point, you would connect a wander lead to one of the conductors of just one leg of the ring, then go to each socket-outlet in turn and measure continuity.
If there are 10 socket-outlets, the mid point will be somewhere between the fifth and sixth highest readings.
 
Im currently studying electrical and im up to dead tests.

ive reached continuity of ring final circuit on my scenario cd , in therory i understand the procedure and what to do but im a little un sure on finding the mid point on the sockets .

please can sombody go threw it step by step in detail

thanks

Step by step detail, and fully illustrated, the definitive answer to your post lies within IET Guidance Note 3. Invest £30, and it will serve you well. it would take me an age to write down the full procedure, but if you get the book, then you will always have it to refer to.

Cheers.............Howard
 

Reply to Continuity of ring final circuit..... can somebody help please !!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, Im new to fault finding, Im on a job where there is no live to live continuity on the ring final circuit which supplys the sockets to the...
Replies
8
Views
2K
Hi All! Officially losing my EF forum virginity with this one, and would greatly appreciate any help you guys could throw my way! Through...
Replies
10
Views
16K
Ok guys been asked help mate out but i think he has done his install wrong but as misplace my regs book cant find exact regulations he...
Replies
21
Views
8K
Morning fellas. I know from regular visits to this website that we have some rather intuitive Sparkie’s on here so I thought I’d join in the fun...
Replies
34
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock