Discuss Continuity Testing reliability in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
29
Friday I was getting continuity readings from my tester which start with a reasonable figure then drop off the scale to 0.00. This tended to occur more on the existing circuits rather than on new circuits. can someone shed any light on this?
 
Friday I was getting continuity readings from my tester which start with a reasonable figure then drop off the scale to 0.00. This tended to occur more on the existing circuits rather than on new circuits. can someone shed any light on this?

Iffy test meter, Iffy connections
 
Low battery?

I also changed batteries on Friday.. which helped at the time.

today I'd like to check the tester out with calcard but could never get to grips with it because at the first stage I fell over. on the back of the cal card you are supposed to record bench mark readings given to you from the certificate of calibration. With the continuity no of the ranges on the back of the card were tested. The card wantd

0.25 ohm
0.5 ohm
1 ohm
2 ohm
5 ohm

off the cert I had under a heading of continuity resistance

20 ohm range
20 ohm range
200 ohm range
2000 ohm range

with IR the card wanted

0.5M
1M
2M
10M
20M

cert had

1 Mohm
10 Mohm
190 Mohm

with tolerance, applied value and reading I guessed I had to record the reading on the calcard so the only value that matched the card was the insulation resistance of 1 Mohm @ 500v which reading was 1.01 mohm.
 
I also changed batteries on Friday.. which helped at the time.

today I'd like to check the tester out with calcard but could never get to grips with it because at the first stage I fell over. on the back of the cal card you are supposed to record bench mark readings given to you from the certificate of calibration. With the continuity no of the ranges on the back of the card were tested. The card wantd
Not quite with you? Using your calcard for the first time, its assumed your MFT is newly professionally calibrated.

Then with your MFT test the insulation and continuity readings you obtain from the card, that your MFT displays (these are recorded on the back of the calcard). From there on in, your should obtain the same readings. If they are 10% out, time to get your MFT re-calibrated or three years, which is either sooner.

The certificate, isn't that to record your monthly checks?

Re fluctuations in your readings, if your MFT dos this against a know resistance i.e. your calcard, time for a visit to the repair shop.

https://www.niceicdirect.com/WebRoo...CA90/69D4/8EC2/0A0A/124C/80C3/Information.pdf

Or have I read you wrong?
 
Last edited:
Not quite with you? Using your calcard for the first time, its assumed your MFT is newly professionally calibrated.

Then with your MFT test the insulation and continuity readings you obtain from the card, that your MFT displays (these are recorded on the back of the calcard). From there on in, your should obtain the same readings. If they are 10% out, time to get your MFT re-calibrated or three years, which is either sooner.

The certificate, isn't that to record your monthly checks?

Re fluctuations in your readings, if your MFT dos this against a know resistance i.e. your calcard, time for a visit to the repair shop.

https://www.niceicdirect.com/WebRoo...CA90/69D4/8EC2/0A0A/124C/80C3/Information.pdf

Or have I read you wrong?

I understand a bit better now having re read the instructions for cal card seems the testers continuity is out somewhat, it is nearing its annual calibration date anyway.
 
I understand a bit better now having re read the instructions for cal card seems the testers continuity is out somewhat, it is nearing its annual calibration date anyway.

This shows the value of keeping checks on your tester. The problem is now that not only is your tester not fit for using at the minute, but also the tests you have made recently may be wrong. Daz
 
I understand a bit better now having re read the instructions for cal card seems the testers continuity is out somewhat, it is nearing its annual calibration date anyway.
I had fluctuations with readings with my Megger 1730, which I eventually realised it was a problem with one of its terminals requiring repair. Fortunately it was still under warranty.
 

Reply to Continuity Testing reliability in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
724
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
259

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock