  1. 7671
    Offline

    7671 Regular EF Member

    Location:
    south
    Just finishing a rewire, customer not sure on hob and cooker at design stage so I went for 2 circuits with 6mm withe 2 32amp rcbo's. Hob and cooker 5 meters apart. Now induction hob and oven have arrived onsite and both suggest a 13amp supply is suffice. Should I downgrade the rcbo's to 16amp and hard wire into plate or exchange plate for non switched fused spur and leave rcbo as is
     
  2. simpson93
    Offline

    simpson93 DIY

    Location:
    LONDON (barnet)
    Do they come with plugs?
    Might not want to void a warranty single sockets might be better

    Also 13amps seem quite small for an induction hob unless it’s a 2 ring hob.
     
    • Dislike Dislike x 1
  3. davesparks
    Offline

    davesparks Forum Mentor

    Location:
    guildford
    How on earth are they going to void a warranty?

    Are you referring to that utter nonsense about removing a moulded plug voiding the warranty on a whole appliance?
     
    • Like Like x 1
    • Funny Funny x 1
  4. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    what are kw for the induction hob &the oven ?
     
  5. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    what ear. ;)
    o,boy.
     
    • Funny Funny x 3
  6. GeorgeCooke
    Offline

    GeorgeCooke Regular EF Member

    Location:
    UK
    The RCBOs are to protect the cable not the thing on the end of it. 32 amp RCBOs are OK for 6mm cable. No need to downgrade.
     
  7. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    If they come with plugs, change the outlet plates to 13a sockets and plug them in
     
    • Agree Agree x 5
  8. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    [​IMG]
     
    • Funny Funny x 5
  9. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
    Put single socket on Instead of cooker outlet plate
     
    • Agree Agree x 2
  10. TJ Anderson
    Offline

    TJ Anderson Forum Mentor

    Location:
    Derby
    Single oven will be ok.Customer has bought the wrong hob. 13A induction has to load share to work with such limited capacity. They should have bought the full blown 7Kw + model. They will hate what they've bought as soon as they use more than one hob lol.
    As said above, leave the 32A RCBO's place and Spurs or plugtops will be ok.
     
  11. GeorgeCooke
    Offline

    GeorgeCooke Regular EF Member

    Location:
    UK
    Actually you will need complete plugs, not just the tops.
     
    • Funny Funny x 3
    • Like Like x 1
  12. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    That’s not quite true. I got simarly lambasted a few years ago on this very subject, and so did some ‘extensive’ research for myself. :)

    Most of the manufacturers don’t give a hoot if you cut their moulded plugs off. However, I did find one or two that did. There were also some that required their original lead replaced, with an manufacturers one, if that is damaged.

    Unfortunately, I never retain my research, so can’t tell you who was being a bit fussy. But recommend you read the instructions before getting out your snips.
     
    • Informative Informative x 1
  13. GeorgeCooke
    Offline

    GeorgeCooke Regular EF Member

    Location:
    UK
    At the end of the day the manufacturer's warranty is in addition to your legal rights. Your legal rights won't be affected by removing the plug. Your legal rights extend to six years as against the manufacturer's typical one year.
     
    • Optimistic Optimistic x 1
  14. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    I knew as soon as the word 'plugtop' was mentioned that George would be along. Any how, must dash as I need some MR16 bulbs.
     
    • Funny Funny x 3
  15. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    don't be silly, you plant them in february/march. use the money for beer.
     
    • Agree Agree x 1