hell there

just after a little clarification really ,when wiring a seperate hob and oven as i understand it both units can be wired directly from the ccu via outlet points for both hob and oven.

if the oven is below 3kw and (manufacturer states needs to be fused at 13A if plugged into a socket or 15-20amps if not) this is where i need a little clarification as two obvious installation options are available

option 1/ run a 6mm cable to a switchfuse spur(fused accordingly) and via 2.5mm to outlet point.

option 2/ run a fused spur from the existing kitchen ring main and directly plug hob

i must admit i would prefer to use option 1 just wondered if anyone had any thoughts or suggestions
 
What i have done in the past and ONLY if the supply cable is sufficiant to supply both hob and oven , i have removed the cooker connection plate installed a dual patress linked the 2 with 6mm and reconnected the cooker connection plate for the hob and added a fused spur for the oven and that was an oven less than 3KW as anything 3kw or above should be on its own circuit
 
very similar to my preferred option nick when having to fuse down from ccu. However i dont see the need to run a dedicated circuit for a seperate oven over 3kw. As long as the ccu is supplied with a cable capable of carrying the rated load of both the oven and hob. As the OSG states a single ccu can be used to supply more that one cooking appliance as long as both appliances are within 2m of ccu. For example if you had a 5kw hob and a 4kw oven. there is no reason why both cannot be supplied from the ccu. as long as the circuit supplying the ccu is appropriately fused and sized.
 
Agreed. Perfectly acceptable electrically.

Except that you have to follow MIs and it is unlikely that the recommended amperage would allow this.
 
yes geoff manufactures fusing requirements have to be considered, so the addition of a fsu on oven or hob may be required, still cant see the need to run a extra dedicated circuit, unless the hob and oven are very high powered devices, OSG states that a 15kw circuit should be able to be run from a 30/32a protected circuit.(diversity applied)
 
Oh no. I didn't mean you would need extra circuit.

Just that if using the appropriate sized cables you wouldn't need to fuse down - but MI require that you do.
 

Reply to cooker circuit in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
590
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
664
Cooker circuit has B40 MCB in the CU for the cooker, confirmed wired to the cooker outlet throughout, via a cooker switch & socket with a 10mm...
Replies
7
Views
1K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock