    essex
    6mm to kitchen.

    Separate hob and oven. Rating combined just under 13000w

    Am I right in applying diversity and the two appliances sharing the same supply.

    45a dp switch off to two ccu's

    32amp mcb 60898
    6mm supply cable


    T.i.a
     
  2. Richard Burns
    Offline

    Richard Burns Respected Member

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    Should be OK
    ((56A - 10) *30%)+10=24A
     
  3. Midwest
    Online

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I would apply diversity separately, to the two appliances.
     
  4. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Are you a real electrician?
     
  5. 2wireit
    Offline

    2wireit Active EF Member

    Location:
    essex
    Pete do you have any positive input? I far from know everything. Thought you could ask advise on here ??
     
  6. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
     
  7. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    if you are a spark ,then you should not be asking that question!
     
    • Agree Agree x 1
  8. robd
    Offline

    robd Electrician's Arms

    Location:
    East Anglia
    The onsite guide covers the question
     
    • Agree Agree x 1
  9. 2wireit
    Offline

    2wireit Active EF Member

    Location:
    essex
    Got no books to hand I'm away. Job is am tomorrow. So thought I'd ask as not done domestic in a while. Advise would be great as to confirm this is ok. I remember reading up about diversity for cooker supplies. Thanks. Don't be to hard on me please
     
  10. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    32A MCB to 6mm T/E ( assuming not run through a load of itchy-poo) to 45A isolator to dual (or 2 separate) CCU, 1 to hob, 1 to oven job done get paid ..next.
     
    • Like Like x 2
    • Agree Agree x 2
  11. Pete E
    Offline

    Pete E DIY

    Location:
    N Wales
    What about the case where the oven comes with a 13amp plug on the end?
     
  12. davesparks
    Offline

    davesparks Forum Mentor

    Location:
    guildford
    Chop the plug off and proceed as normal, a 13A plug on a fixed appliance not subject to overload is just an unnecessary potential point of failure.
     
  13. 2wireit
    Offline

    2wireit Active EF Member

    Location:
    essex
    Job done. thank you for advice telectrix. combined load was actually 10.10kw. upon install.

    hob 5700kw
    and oven 4400kw.

    just thought id leave feedback !
     
    • Like Like x 1
  14. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    yhat adds up to 10,100kW. you'd need Wylfa Nuclear Power Station to run that.
     
  15. 2wireit
    Offline

    2wireit Active EF Member

    Location:
    essex
    Sorry 10,100w lol. Too many beers!
     
Loading...
Similar Threads - Cooker diversity second Forum Date
Stoves range cooker tripping RCD Electrical Appliances Forum Yesterday at 8:49 PM
Exposed live wire in cooker wall socket Electrical Forum Feb 9, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job