Discuss Corroded swa gland - garage CU in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
41
Hi,

Have a garage consumer unit supplied from the house CU via a 6mm 2core swa. I noticed this morning the gland entering the garage CU was loose so opened it up to tighten up the gland lock nut. Unfortunately it appears the gland as it enters the garage cu has corroded and brocken away from the lock nut. It's only been install 3 years and the other glands show no sign of corrosion. I have suspicions as to what has caused it but would like some other views on the matter. Pics attached. Thanks

IMG_5674.JPG

IMG_5675.JPG
 
That's what I was thinking. As you have probably already established, the swa is utilised as Cpc. As a consequence there is no separate dedicated bonding provided within the garage I.e. Earth rod / nest as this isn't required, however; one of the outgoing ways from the CU serves an external metallic lighting column. Could this accelerate the corrosion?
 
Thanks all, the CU is aluminium and I thought the gland was copper / brass. It's the gland which appears to have failed, in this instance at the point it passes through the Al CU. I can't have this happening again, who knows how long ago it actually failed. I'll investigate Al glands.
 
What else is connected to the earth bar?

Did you pull the shroud back from the gland? Was there any sign of moisture ingress?

Uncoated brass and nickle-plated brass glands are designed for use with dissimilar metals ie steel armour strands which are galvanised so I don't see how the gland having a galv nut would cause such advanced corrosion in such a short time.

If the CU enclosure material is ferric or steel based then moisture under the gland nut could cause it to rust, especially where the paint might have been cleaned off to ensure good contact for the earth ring. Rust causes expansion (think of windscreens that crack when rust gets under them on a car) which could have cause the gland to split.

It's worth noting that moisture around the gland could be caused from it dripping inside the enclosure but could also be coming from inside the cable sheath by capillary action. so I'd disconnect the armour at both ends and megger it to a known earth, if it fails then start digging to find the cable sheath damage.
 
I feel fairly sure the BG IP rated boards are cast alloy (not sure what alloy) not aluminium, the metal does not respond like aluminium and it would not be all that "non combustible" as aluminium is highly reactive (when exposed) and has a low melting point.
A current flowing or induced in the metal of the CU would increase the corrosion rapidly and I would agree with Marvo about the possibility of water in the shroud, though it does look like it is coming from above.
 
The garage is usually only a single brick skin construction if the wall outside face brickwork is getting a lot of rain on it due to it's orientation water will penetrate through and rainwater/dampness may be coming from where the fixings are.
 
My immediate thought when I saw the obvious corrosion was internal condensation but there's zero evidence of it anywhere else, all the other metalic items in the photo are bright and shiny plus there's no signs of drip/splash marks on any other surfaces, everything else in the photos is spotless. This is why I thought it likely the moisture was coming internally from the SWA cable itself and certainly worth a quick IR test of the disconnected armour to earth.

It would be great if you could give us more info after your next visit Leyland, I'm very interested to here the final solution on this one.
 

Reply to Corroded swa gland - garage CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
13K
I would appreciate peoples thoughts on fixing this earthing setup to correctly separate PME & TT: Setup: Workshop at the bottom of a long garden...
Replies
31
Views
10K
Background: Served my apprenticeship 1964 to 1969 with NORWEB but not been directly employed in the industry since then. I have just laid a 10mm...
Replies
27
Views
9K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock