A 230 volt 14 kW domestic storage heater, installed in a house is to be supplied by a 15m run of PVC insulated and sheared cable, clipped to a surface. The circuit is to be protected by a BS 3036 fuse and the value of external impedance is 0.85 ohms. Calculate the minimum size cable that can be used for this circuit to comply with shock protection.
Ib: 60.87
In: 100
It: 60.87
Iz: 65 No correction factors...
csa= 10mm2
VD = 4.4 x 60.87 x 15/1000 = 4.02 (VD is below 11.5)
Max Zs = 0.53 and that is already higher than the Ze? What should I do...
Ib: 60.87
In: 100
It: 60.87
Iz: 65 No correction factors...
csa= 10mm2
VD = 4.4 x 60.87 x 15/1000 = 4.02 (VD is below 11.5)
Max Zs = 0.53 and that is already higher than the Ze? What should I do...