Discuss CPC for shower! in the Australia area at ElectriciansForums.net

Reaction score
7
Hi guys, i just changed a 8.5kw electrical shower for a friend, the live is 6mm2 and i believe it is fine, the only thing is the cpc, looks like 1.0mm, at most 1.5mm, i checked codes, but still not sure about it, is this cpc ok?

cheers
 
Hi guys, i just changed a 8.5kw electrical shower for a friend, the live is 6mm2 and i believe it is fine, the only thing is the cpc, looks like 1.0mm, at most 1.5mm, i checked codes, but still not sure about it, is this cpc ok?

cheers

First response to a post for me. Assuming both protective and line conductors are copper, then according to table 54.7 in regs (pg 130 in mine), suggests csa of protective conductor should be (at least) same as line conductor?

Thats the way I'm reading it anyway, but have to admit I've never seen a 6mm cable with a 6mm earth? Having said that, if you can imagine nearly 40amps running down your skimpy cpc in a fault condition then it doesn't sound ideal to me!

Pat
 
Last edited by a moderator:
First response to a post for me. Assuming both protective and line conductors are copper, then according to table 54.7 in regs (pg 130 in mine), suggests csa of protective conductor should be (at least) same as line conductor?

Use the adiabatic equation.
 
Hi,
Whats the length of the cable and how is it run ( under floorboards, clipped direct etc ).

You said its old cable, is it the old colours Red, Black ??

You also mentioned 8.5kw shower, so that equates to 36.95 amps ( ib ), so depending on your fuseboard, you need at least a 40amp mcb.

So work out your current -carrying capacities, volt drop and adiabatic to get correct cable selection. You should really know what size cable you have selected, as this can have a big effect when the shower is on ( over heating the cable etc ).

Hope this helps,
Sav
 
Hi,
Whats the length of the cable and how is it run ( under floorboards, clipped direct etc ).

You said its old cable, is it the old colours Red, Black ??

You also mentioned 8.5kw shower, so that equates to 36.95 amps ( ib ), so depending on your fuseboard, you need at least a 40amp mcb.

So work out your current -carrying capacities, volt drop and adiabatic to get correct cable selection. You should really know what size cable you have selected, as this can have a big effect when the shower is on ( over heating the cable etc ).

Hope this helps,
Sav

i only changed the shower and did not touch anything else. the colors are old: read and black. 6mm.

i could find easily the minimum size of main bonding conductor is 10mm, but just cannot find minimum requirement for cpc in the bs7671, is 1.5mm really ok?
 
i have not done the adiabatic equation, but guessing as some of the results i got previously from using that equation, they maybe , yes .

BUT, you must make sure you do it properly i.e supply protective device etc.....

Sav
 

Reply to CPC for shower! in the Australia area at ElectriciansForums.net

Similar Threads

I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
790
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock