Evening,
Just joined upto this forum after a search online for some info, hopefully someone can help me?
I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB roughly 100m away.
My concern is that it appears they have not run a separate earth and are relying on the armouring as the CPC. I believe it should have a 25mm earth ran in alongside the SWA?.
My other problem is that the cable is now burried underground and has a tarmac road above it ect.
What are my options?
Thanks in advance
 
Armour will be acceptable as the cpc however the length could be a factor as to achieving your disconnection time, calculations required IMG_2860.JPG
Evening,
Just joined upto this forum after a search online for some info, hopefully someone can help me?
I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB roughly 100m away.
My concern is that it appears they have not run a separate earth and are relying on the armouring as the CPC. I believe it should have a 25mm earth ran in alongside the SWA?.
My other problem is that the cable is now burried underground and has a tarmac road above it ect.
What are my options?
Thanks in advance
 
Evening,
Just joined upto this forum after a search online for some info, hopefully someone can help me?
I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB roughly 100m away.
My concern is that it appears they have not run a separate earth and are relying on the armouring as the CPC. I believe it should have a 25mm earth ran in alongside the SWA?.
My other problem is that the cable is now burried underground and has a tarmac road above it ect.
What are my options?
Thanks in advance

Presumably you have calculated that a 25mm copper conductor is required and not just guessed this?
 
Davesparks i was referring to table 54.7 of bs7671 which states if S>35 and the protective conductor is the same material as the line conductor this is S ÷ 2
S = 50mm
50 ÷ 2 = 25mm

So no calculation then, just using the Table which gives an oversized cpc. Not that there is anything wrong with using the table for design work, but when assessing compliance of an existing setup you should do the proper calculation with the adiabatic equation to make certain if the answer from the table isn't acceptable.
S is not the same material as the line conductor in this case so why have applied that part of the table anyway?

Did you even go as far as assessing the suitability of the armour based on the table 54.7 requirements? Or did you only look at the required size of a copper cpc??
 

Reply to CPC size of SWA Armouring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
https://gadsolutions.biz/regulations/swa-as-the-cpc Anyone know how reliable the tables on this website are for determining whether the armouring...
Replies
13
Views
3K
Hi all, I’ve been given 3 flats to re wire and i was looking for advice on the correct size Swa to use. There will be 3 meters installed by the...
Replies
12
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi all. Been asked to join a couple of 25mm 4 core Swa's underground so am using a couple of torpedo's. This is probably a basic question but one...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock