We all know this is wrong and breaches regulations and manufacturers instructions.

Good tread on this:
https://talk.electriciansforums.co....link-on-smoke-alarm-circuitwhat-would-you-do/

However the question is does it warrant a C2 over C3?
My recommendation is going to be radio link and reinstate CPC or rewire with 3-core. But what code to give?

GN4 recommends a lighting circuit supplying only class 2 as C3
 
if you give it a C3, then the customer gets a satisfactory report ........ and who's to say they will do anything.

Whether you can justify a C2 is somewhat debatable, except all fixed mains cables should have a CPC in them which is functional - so a C2 imho

EDIT: I think the GN4 advice alludes to lighting circuits without CPC's and your installation has clearly been done incorrectly so the C3 is not really an option.
 
debatable here. if the cpc is used as the interlink, then it's not carrying 240V. not right, but a C2 might be a little harsh.
 
as a non-electrician, I have a question...
if the cable used to interconnect is at mains voltage, shouldn't it have a cpc, even if the individual detectors don't need one?

If the detectors were non mains supplied, then any 3 core cable would do the job, but T&E presence might cause unnecessary confusion to someone opening up at a later date?

Radio interconnect is an option (a good one, imho) but not an option in rented housing...but in Scotland it will be soon, thankfully.

Hope i have explained that correctly...
 
There is a DIY fitted duel RCD board with all the circuits on one RCD and the second empty!!! Except for 2 lighting circuit non RCD protected.
Idiots!
I've got it down as C3.. Sup bond in place
 
It's not a separate cable the've used Pirate, it's T+E with the CPC over sleeved live and used as interconnect. Hence the problem, no CPC and no basic insulation for interconnection
 
Well every point on a low voltage circuit has to be provided with a cpc (reg?). So that's that surely code whats is face.
 
Last edited:
A few years ago I did a periodic at a charity shop which had Part 6 detection. The shop was in darkness when I showed up because the manager was waiting for me to turn up to show me a trick. As she switched on the shop area modular fluorescents the detectors triggered. Turns out the interconnection was the cpcs which were also connected at some point to earth.
 
Interesting one here.

My initial reaction is a C2. Then when you think about it it is 8-12 volts DC that only has a single layer of insulation.

Would I C2 a speaker cable in the wall? No of course not.

If everything is also Class 2 then again I fail to see how to code this.
 
My initial reaction is a C2. Then when you think about it it is 8-12 volts DC that only has a single layer of insulation.

But 12V with respect to what? A live conductor. If you connect one side of a PP3 to mains, the PP3 is still 9V but now it's potentially lethal (pun intended).
 
as a non-electrician, I have a question...
if the cable used to interconnect is at mains voltage, shouldn't it have a cpc, even if the individual detectors don't need one?

If the detectors were non mains supplied, then any 3 core cable would do the job, but T&E presence might cause unnecessary confusion to someone opening up at a later date?

Radio interconnect is an option (a good one, imho) but not an option in rented housing...but in Scotland it will be soon, thankfully.

Hope i have explained that correctly...

Yes all cable installed shall have suitable cpc travelling with it. I'm not aware of battery alarms that ask for wire interconnect, so not thought about that one. It does annoy me that some folks steal it for some other purpose. Radio clearly the way forward for difficult situations :) .
 
The cpc in this case, has a distinct possibilty of making contact with one of the Live conductors in the detector and or the cable itself, if the cable become damaged, the cable is not being used as it should, so it should be replaced with a cable that is fit for purpose.
It's an inherently dangerous thing to do in my bok, would you use the cpc in respect of the strappers in a 2 way lighting circuit, well I know I wouldn't with that in mind you should code it as dangerous.
 

Reply to CPC used as interconnect on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Prompted by the other thread.... I had a slight dilemma on this topic a couple of days ago. Three mains smoke alarm bases, on their own circuit...
Replies
9
Views
2K
Just wanted to get peoples opinion regarding a job ive been asked to do. The customer wants improved fire detection in there property, which is a...
Replies
19
Views
2K
D
I carried out the new PIR / condition report today and found a diy bodger had added two way light switching, in flex ,using the cpc as a live, in...
Replies
25
Views
14K
Graeme Harrold
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock