Discuss Current generation under control in the UK Electrical Forum area at ElectriciansForums.net

A cheap stick welder gives you a stepdown transformer with a secondary good for 100-200A. That has its own current control (using a magnetic shunt operated by the handwheel) but it's not that controllable.

Another way to get heavy current at very low voltage is to make your own stepdown. Wrapping a few turns of heavy cable through the open centre will create a very low voltage, high current secondary. E.g. a 500VA tranny works at around 2 turns per volt, so two turns of 25mm² will give you a source of 100A or so at 4V. It won't be a perfect transformer because such a sparse winding won't couple well, but it will work. You can make a better job by unwinding the original secondary and filling the space with multiple paralleled cables. 4V is sufficient to pump that 100A through any object under test up to 0.04Ω.

The adjustment can then be achieved, as with the welder, using a separate variable voltage transformer a.k.a. Variac.
 

Reply to Current generation under control in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
518
Good day all, I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz. I'm managing a...
Replies
3
Views
1K
How should grounding be made to a 20kVA single phase generator set feeding a domestic property via a manual change over switch? At the generator's...
Replies
17
Views
3K
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
hi all, What are your thoughts on how the 6231 cables been terminated? Will aluminium cause eddy currents? Thanks
Replies
37
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock