Posting a message to the forum will remove the above advertisement
  1. angel While you're here, woud you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

Discuss Curve (Denmans) RCDs in the Electrical Tools and Products area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. a-z electrics
    Offline

    a-z electrics Regular EF Member

    Location:
    Exeter area
    Business Name:
    A-Z Electrics
    Anyone had problems with these rcds? Control Gear Direct, 30mA, 63A 2 pole..

    I recently bought two 10-way dual rcd boards from denmans.. first one had an rcd which didnt trip on test button, even with load removed. Second rcd didnt trip under 300mS, but button worked.

    Swapped them for the rcds in the second board I had (lucky me, I thought).. one rcd was ok but second one also had trip time problem. swapped the rcds around and the problem followed the rcds.

    Got denmans to hotfoot replacement two boards that day... one rcd no trip on test button, the other had trip time problem!
    The rcd which "worked" ok, I subsequently found to be a bit intermittent also on trip time. Once i put it on x2 test it seemed to settle down. but also the test button sometimes takes a while to trip as well! ie had to hold it down for a second or two.. the test results when working show no unusual results, all appliances were disconnected.

    I did wonder if my tester (metrel 31000) was beginning to play up but worked ok at home and was only calibrated a few weeks ago.
    I also put in the only other rcd i had with me, a Hager, and this has been fine.
    Control Gear have posted to me 4 replacement rcds with test results, so ill see what happens..

    First time ive had NO Trip problems, usually the other way...
     
  2. Phil Thompson
    Offline

    Phil Thompson Let us light up your life! Electrician's Arms

    Location:
    Newtownards
    Business Name:
    Brite Spark Electrical
    I’ve been to 3 jobs in past 7 days, with a total of 7 RCDs, 4 in 1, 1 in another, and 2 in the job today.

    All 7 wouldn’t time out. Phoned my rep and he said that’s why his place don’t sell them as they wouldn’t time out, that’s the way they came from factory, every one of them.

    Anyone else found this?
     
  3. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Are you testing at the RCD terminals? If so there are a few manufacturers that I can remember off the top of my head but you add a short bit of cable in to the equation and they are fine.
     
    • Agree Agree x 1
  4. Phil Thompson
    Offline

    Phil Thompson Let us light up your life! Electrician's Arms

    Location:
    Newtownards
    Business Name:
    Brite Spark Electrical
    At Sockets in the properties.
     
  5. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    I would of checked at the terminals to confirm.
     
    • Like Like x 1
  6. Richard Burns
    Offline

    Richard Burns Trusted Advisor

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    I would agree with Lee above, test the RCD at the terminals with no load connected.
    (Eaton RCBOs need to be tested from the cable entry rather than the terminals as the sensing coil is above the terminal.)
    I have used some Lewden, curve, Denmans, CGD RCDs but I have not yet had a problem with them. They are bottom of the price range but they should operate OK.
    Having seven fail at one installation sounds on the edge of possibility.
     
    • Like Like x 1

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job