Discuss Cut-out fuse shared by 2 properties in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

E

elementps

Hi All,

Been to look at a job, where customer wants to install 9.5kw shower. 3 Bed 2 storey flat.

Calculating the load on board at present with diversity comes out at 68.8A, if the shower was added calculations came to 94.6A.
Looking in the meter cupboard, the supply splits to 2 meters after the incoming fuse, supplying the flat opposite. Is this common practice (not something I have come accross before)?
So as I see, the 100A supply is divided between the 2 flats, how can you possibly determine load, with the unknown of what next door are using? Any ideas on how to continue?
 
Personally I would look again at the max load figure your using. It seems very high for the type of property.?
I know there's no diversity available on showers... However putting a practical / real world angle on it, it's unlikely that you will have 60 odd amps worth of demand happening, AND the shower operating on top of that..?
 
There are many and various methods used for calculating max demand, including the one you used.
Personally I should go by the OSG figures for diversity.
The method you used is a bit of a blunt instrument in my opinion.
I think you will find that the "true" figure will much less in reality.
 
I always used a formula given to me from an old DNO engineer and that is add up the protection devices in use and multiply by 0.4

so if you had 32+32 +6+6 +40+16 = 136* 0.4 = 54amps

And you would normally still be lucky to see even that 54A!! Even if you did, it wouldn't be for long, ....minutes at most!! lol!!

But Malcolm's method is as good as it gets and is a commonly used assessment of max demand. On the other hand using diversity figures from BS7671 isn't a very good idea, it will always give you final figures that, come nowhere near reality... The only one that has any real meaning to it, is that covering cooker loads upto 15KW....
 
Thanks guys, I do agree with the opinions on diversity calcs, always come out at very high values.
Any ideas on the shared cut-out fuse??? Anyone had to deal with something similar before?
 
Ive seen it a few timers. Metering technicians dont like it, and usually moan/blow the job out.

Not sure how you'd get it altered, by speaking to UKPN (in London) I suppose.
 

Reply to Cut-out fuse shared by 2 properties in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
802
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I would like some advice please. A friend of mine has moved into a small flat. There is no Gas supply to the property and so is looking into...
Replies
19
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock