I have a project in a hotel that has a DALI control system

We are supplying LED downlights that are dimmable on the DALI protocol but they also want other lighting ground lights and wall lights that do not need to be dimmed.

Question is will they still work on the standard LED drivers or do these need to be DALI as well even if they are not being dimmed?

Any help appreciated
 
So do you want the DALI system to switch the other lights together with the LED downlights or can they be completely separate?
Either way you can get a DALI switching unit to switch whatever kind of load you want, it just makes things a bit more complicated.
 
It will be separate downlights in the hotel interior areas, but they also want the ground lights and floodlights on the DALI system but just standard switching, so totally separate circuit.

So would you advise DALI drivers on the exterior non dimmable lighting as well?
 

Reply to DALI Control systems - Do i need different drivers? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
721
I've been asked to quote for track lighting replacement in a London art gallery that's suffered extensive water damage from the floor above...
Replies
1
Views
1K
Hey folks, i work for a relatively small company, but we are doing some big jobs. And right our headache is taking over outdoor lighting...
Replies
4
Views
1K
I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
566
Hey, with regards to DALI Emergency Lighting Automated testing via a control system, does anyone know how best to overcome a fitting that is...
Replies
1
Views
862

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock