gazdkw82

-
Arms
Reaction score
735
I've installed 2x JCC71361 Dali LED panels controlled via an EX-OR lightspot HD PIR.

I seem to be having a real problem with it. The customer complained one of the fittings was flickering ever so slightly. I went back and indeed it was lightly flickering. I swopped the control gear over but the same fitting flickered. I rang JCC who said it must be a faulty panel. However, it's been replaced (and a new driver) and now both are lightly flickering.

Any ideas what this could be? It's driving me crazy. I've tried looking through the parameters of the PIR using the remote control but nothing seems to be obvious.
 
Just double check those setting with data sheets for the driver and the fitting.. very common for the fittings to flash for a mis-match..
Are the new drivers a line for like replacement?
 
Just checked the spec of that JCC fitting..
It is rated at 1050mA, 35 watts

The driver you have linked to is unsuitable
 
If it is not the above as helpfully posted on here we have had this same issue with CP Electronics Dali dimming PIR's where the lights have been flashing it is to do with the natural light coming in a simple reprogramming and it should be sorted.
 
If it is not the above as helpfully posted on here we have had this same issue with CP Electronics Dali dimming PIR's where the lights have been flashing it is to do with the natural light coming in a simple reprogramming and it should be sorted.

Reprogramming? Maybe turn the light adjustment off?
 
It's a slightly different driver. It's a DC Maxi Jolly. It seems to be capable of powering the fitting.

I'm still unsure why JCC have said it needs to be 1,2 and 3 in the on position. That's 48v (sec) 850ma and 650ma.

Seem right?

Dali lighting help with issue Screenshot_20190522-143932 - EletriciansForums.net
 
The information jcc have given you will probably be for the drivers that come with their fittings..
 

Reply to Dali lighting help with issue in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock