Discuss data cable buried direct in concrete in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
I've been asked to look at a job (total shambles) they've given the other sparky the boot because of his poor workmanship. I've honestly never seen work so bad. one of the main issues is a load of floor boxes have been chased in, the data cabling has been buried direct in concrete, is there any issue with this providing the cables test ok? the concrete will not affect the cabling?

cheers
 
If I understand correctly - the concrete floor was in place, then the chase was made and the cables were cemented in?
 
If I understand correctly - the concrete floor was in place, then the chase was made and the cables were cemented in?

concrete floor was chased out, cables place in and then covered with concrete. Its rubbish, but if it all tests ok, i can let the builder know that the cables won't deteriorate in years to come?
 
Probably the most hazardous period was when the cables were cemented in - risk of conductors being cut or insulation removed by a sharp bit of gravel. If it tests ok for continuity, insulation resistance and function now, it's probably going to be ok, but I wouldn't be putting a warranty on it. If construction is still in progress, perhaps float the idea of either running a backup conduit or even putting it right?
 
What testing have you done to ensure the data cables are OK?

DC checks will only show that there is continuity and no short circuits but if they are data Cat 5e or Cat 6 cables there is a chance that the high frequency characteristics of the cable have been impaired. The chances of problems are very small and will, to an extent, depend on how long they are (standards for data networks allow up to 90 metres) but you might give a future IT person a headache if the data cable will not handle the data signals at 1 Gigabit data rates without errors (250 megabits per second down each of the 4 pairs). It would need specialised equipment to ensure that the cables were up to full specification.
 
Even if it checks out ok now it will go wrong in time, whatever has been done to make good the chases in the concrete will move relative to the existing concrete and the fragile data cables will suffer.
 

Reply to data cable buried direct in concrete in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the...
Replies
6
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
414
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
Hi, Ive had a NAPIT qualified electrician out to install a new feed to the garage along with a new consumer unit in there. Its a short distance of...
Replies
73
Views
15K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock