Ideally, you should swap the RCBOs in the Lighting panel for MCBs, swap the 63A MCB for an RCBO and swap the upfront RCD for a main switch.
Then again, is it really worth it?
The rcbo’s in the lighting panel are specified by the supplier.
Am I right in saying if I do what you say,a N/E fault will still remain,there will be no Rcd to eliminate it.
Also why are we been given rcbo’s that are not DP.
 
In my experience a N/E fault on a circuit which is 'off' is far less likely to have an effect on other circuits when part of a TT system. I always assumed this was due to the much higher N/E resistance at the source of the installation compared to a TNCS or TNS earthing arrangement. I'm sure most of us have experienced the embarrassing [when customers are around] RCD operation when you accidentally short out neutral to earth when working on a circuit ? Well I'm sure that's never happened to me on a TT system.
 
double pole RCBO's will more than likely be double module. Single pole switched neutral RCBO's can def be found in single module size.
The SBS fella does single module, compact height, DP RCBOs with no earth lead. The only ones I know of.
 
I feel like I need to say sorry! Definitely won’t do it in chinese -
I’m going to ask Google translate for my money back (even though It cost nowt!)
Unfortunately for your example, Chinese is also written left to right, top to bottom, same as English! Also there's no direct translation of "yes" as you agree with something by repeating the verb.
A little bit of useful world knowledge;)
 

Reply to DB installed connected & tested in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock