Discuss Dead Testing Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

Rotax100uk

Hello all, i have some dead testing to do, i just have a new megger Robin KMP3075DL and when using it in Insulation test mode (500v - 20Mohm) on 2.5 twin + earth as practice, i test between LINE and CPC and get the reading from the display (up arrow 1) so on my schedule of tests sheets what would be the best result to write down?? (friend told me to draw the infinity symbol) im a little stuck on this one, could anyone advise please
 
>20 as that is what the meter is reading. Do not use the symbol for infinity.
 
thanks thats great for the reply. the result im getting is (UP ARROW and 1) do you think that would be an acceptable result? or would you advise >200M? thanks
 
Your meter according to your original post was set on a 20Mohm scale so you fill in >20
 

Reply to Dead Testing Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
882
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
G
I'm trying to get my head around inspection and testing. When I'm struggling, i often find writing it down helps me to learn it - please could you...
Replies
7
Views
1K
Hey peeps! First of all hoping you all had a sound bank holiday weekend (mine was obviously working and earning the pennies but hey ho)...
Replies
4
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock