    Would cables not clipped causing them to sag be a departure from bs7671
     
  2. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    No, that would be a defect, an ommision or non-compliance.
     
  3. sparkymatt1987
    Offline

    sparkymatt1987 Guest

    Ok thanks. I sometimes get lost with what is a departure from bs7671
     
  4. sparkymatt1987
    Offline

    sparkymatt1987 Guest

    So am I right in sayin I shouldn't be putting anything in the 'details of departures from bs7671' when doing an electrical installation certificate for the addition of a new circuit as the certificate is covering the work I have done and what I have done does comply?
     
  5. IQ Electrical
    Offline

    IQ Electrical Electrician's Arms

    Check out Regulation 120.3
     
  6. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    A departure is something that is intended by the designer, does not comply with the Regulations, but the designer attest will offer the same degree of safety as would be achieved by compliance with the Regulations.
    For example:
    If changing a CU where there is no CPC on the lighting circuit, the advice given in the ESC BPG is to install a 30mA RCD, use class II fittings andplace a warning at the CU.
    Such would be a departure.
    Anything else would either require rectification before the Certificate was issued, or a note in the section for comments on the existing installation.
     
    Last edited: Feb 23, 2012
Loading...
Similar Threads - Departure bs7671 Forum Date
Old copies of BS7671?... Electrical Forum Yesterday at 11:40 AM
BS7671-2018-Corrigendum - Amended! Electrical Wiring, Theories and Regulations Dec 26, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job