Discuss Designing and calculating in the UK Electrical Forum area at ElectriciansForums.net

magnoliafan89

-
Esteemed
Arms
Reaction score
540
Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??
 
Double check the table you are using as well...
 
Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??
A good video to get you started, there are plenty more, but this Bloke is one of the best, imo
 
Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??

Hi,

Im currently doing the 104 assignment for the hotel, cafe & pool.

Got this from my training provider which might help:

Screenshot_20181101-173314_Gallery.jpg
 
As no one has commented "Spoon, not only are you stunningly good looking but your observation skills are second to none.." on my post #5, I thought I'd better expand on it....
Check out reg 512.1.5
 

Reply to Designing and calculating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
947
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock