Discuss Differences in Zs between left and right sockets in a double outlet in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

S

SW1970

Hi, did a PIR on a house yesterday, early 90's build with lots of MK double sockets. Strange goings on with Zs - the left and right sockets were significantly different on many of the outlets, e.g. 0.4ohm left, 0.6ohm right. Any thoughts - dodgy batch? For a piece of brass or copper about 8cm long can't understand why readings are so different. Thanks, SW
 
Yup, resistance and use of the socket would create this situation.

One was probably used more that the other, which means the unused one may have oxidised slightly.

Push the plug of your tester in and out a few times of the suspect socket.
 
Ok, furthering this on a bit; adding some sockets into a ring so carried out testing around the ring to check for spurs, bridges etc. Cheap accessories from 1980s rewire. Readings are still significantly different even after lots of "plug thrusting" (that's my term for a plug giving it big time to a socket, you get my drift). For example:

Before plug thrusting:
Left: 1.4ohm Right: 0.72ohm

After plug thrusting:
Left: 0.97ohm Right: 0.69ohm

If I'm on the lookout for bridges on the ring, I'd expect <0.05ohm difference between different socket outlets on a L and N cross connect test, but with these sorts of magnitudes of differences caused (apparently) by oxidation, this test doesn't have much value.

In this scenario, should it be deemed that the accessory has failed and should be replaced to allow decent readings to be taken? Or any challenges on the 0.05ohm threshold? Thanks folks.
 
Of course, you could always remove the socket front, and measure from the terminals.
I once was at a customer's house installing an extra socket-outlet in their hall, they hadn't long moved in.
The lady of the house unformed me that one outlet of one of her kitchen double sockets didn't work, and asked me if I could change it.
I just removed the plug from the other outlet, plugged it into the defective one a few times, untill it worked.
Probablly not the best course of action business wise.
 
In this scenario, should it be deemed that the accessory has failed and should be replaced to allow decent readings to be taken? Or any challenges on the 0.05ohm threshold? Thanks folks.

I would only fail in this instance if the difference pushed it over the max zs.
If I do a ring test on a house with this problem I usually use my robes to do it as you can scratch the brass inside socket and get a better reading then if you just pushed a plug in.
 
i have also had this problem testing a ring a few years ago as spinlondon said unfortunately you have to remove the socket and test from the terminals. This was on the metallic type sockets and they were brand new, thought my tester was broken.
 
I've got the BS1363 test lead for my MFT, a proper socket test adapter, plus the old "dodgy plug".

The "dodgy plug" has had its pins purposely roughed up to bite through the tarnish on socket contacts.
It's not exactly GS38 but avoids pulling socket fronts off, balance of risk etc

Also the 3kW fan heater comes in handy to clean the switch contacts up too... a few make/breaks under full load generally sorts them out.

Simon.
 

Reply to Differences in Zs between left and right sockets in a double outlet in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock