J

jimmer

On an installation of Metal halide low bays that i fitted a few years ago, some of the fitting are going on and off during the day. Some times they are off for hours. The installation does have heavy industrial machines so voltage spikes on start up or full load could have an effect but i would only expect this to knock out a fitting fo 10 minutes or so. Is it an ignighter issue?
Any help much appreciated
 
It does sound more like a lamp issue, especially if the lamps are more than about 18 months old. even when a full relamp is done there can be some massive variations in lamps from the same batch. This seems to be more apparent with halides than sodium for some reason. Some ballasts can be more sensitive to voltage than others as well, although this tends to be less common than the ignitor/lamps faults. What i've found usually with ignitors is they they either don't strike at all or the lamp doesn't get to full brightness. if it was a brown-out issue i would expect to see more than a few fittings drop out.

hope this helps
 

Reply to Discharge lighting fault finding in the Australia area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
383
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
599
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
668
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock