Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Diversity applied, max load well over. in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. ChrisElectrical88
    Offline

    ChrisElectrical88 Forum Mentor

    Location:
    Norwich
    Seen a couple of threads on diversity and excessive max loads recently.

    Just had a design from a clients for their house. Applied diversity is 196A.

    Having 2 9kW showers install, A 4kW instant water heater, a cinema room, ring main per floor, lighting circuit per floor and ring main for kitchen.

    100A Single Phase Supply
    No chance of another supply.

    Hes already having 2 combi showers as well as the 2 electric so doesnt want to get rid of them.
     
  2. ChrisElectrical88
    Offline

    ChrisElectrical88 Forum Mentor

    Location:
    Norwich
    Also even if i install a priority unit for the showers, its well over.
     
  3. Cid
    Offline

    Cid Regular EF Member

    Location:
    London
    How many people in the household? If they got combi showers can't imagine electric being used frequently
     
  4. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    I'm guessing it's pretty huge if it's got 4 showers and a cinema room.
     
    • Like Like x 1
  5. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    They might be umpa lumpa's
     
    • Funny Funny x 1
  6. ChrisElectrical88
    Offline

    ChrisElectrical88 Forum Mentor

    Location:
    Norwich
    5 people. Ive squeezed it down to about 110A after convincing some changes, showers 7kW with priority board, instant hot water gone and a couple of other things.
     
  7. Vortigern
    Offline

    Vortigern Regular EF Member

    Location:
    England
    Business Name:
    F.H. Electrical
    I expect they will be disappointed with the 7kw showers though when they get in them to shower.
     
    • Agree Agree x 1
  8. Vortigern
    Offline

    Vortigern Regular EF Member

    Location:
    England
    Business Name:
    F.H. Electrical
    Curious about how you calculated diversity. Was it highest MCB + 40% of rest?
     
  9. TJ Anderson
    Offline

    TJ Anderson Forum Mentor

    Location:
    Derby
    Hi Chris. 2 x Electric Showers and 2 off the combi. ....

    Have they got a cold water storage tank and booster set?!
    The water pressure would be an issue!

    Forgetting water for a sec. If you go with a prority unit for the shower and ditch the instantaneous 4kW water heater, can you put your calcs up on here for us to look at?
     
  10. ChrisElectrical88
    Offline

    ChrisElectrical88 Forum Mentor

    Location:
    Norwich
    Diversity was applied using the tables in the OSG. The 7kW showers are for the kids rooms i believe, however he is now considering all 4 showers off a cylender, which if the case would remove any issues i have, he doesnt think more than one shower will be used at any one time anyway.

    Regarding water pressure the owner of the house is owns a plumbing business so ill leave the pressue.

    I can put calcs up if wanted when i get back to the office.
     
  11. ChrisElectrical88
    Offline

    ChrisElectrical88 Forum Mentor

    Location:
    Norwich
    Infact, the following is off some scrap paper:

    Cylender 16A
    1st Floor Ring 12.8A
    First Floor Lighting 3.96A
    Ground Floor Kitchen Diner Ring 32A
    Ground Floor Lounge and Hall Radial 8A
    Ground Floor Lighting 3.96A
    Lower Ground Cinema Ring 12.8A
    Lower Groubd Lighting 3.96A
    Heating 3A
    Alarm & CCTV 6A

    Total is 102.48A
    However the lights will all be LED and shoukd only pull about 6A Total with all switched on.
     
Loading...
Similar Threads - Diversity applied load Forum Date
Commercial Heat pump diversity calculation question Electrical Wiring, Theories and Regulations Mar 12, 2019
Industrial Diversity allowance on sockets based on OSG Electrical Wiring, Theories and Regulations Mar 10, 2019

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job